#214073 - 09/28/14 08:54 PM Code for Junction Box mounted on Floor
dwhite Offline
New Member
Registered: 09/28/14
Posts: 4
Loc: IL
I thought junction boxes mounted on a floor had to have the top flush with the floor. However, a box, along with conduit going over to, and up one wall, was mounted on top of the floor in the classroom I work in in Chicago. It is in a corner of the room about 8" from one wall, and 16" from the other. It is about 2" in height above the floor. I'm wondering if I am mistaken about a floor box needing to be flush, or if there are exceptions I am unaware of.

Top
2017 / 2014 NEC & Related Books and Study Guides
#214075 - 09/28/14 11:32 PM Re: Code for Junction Box mounted on Floor [Re: dwhite]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Floor boxes need to be listed as floor boxes. Then they have to be installed per instructions. That should get you what you need.
_________________________
Greg Fretwell
Top
#214077 - 09/29/14 04:26 PM Re: Code for Junction Box mounted on Floor [Re: dwhite]
Fiver Offline
New Member
Registered: 09/29/14
Posts: 6
Loc: United States of America
The term "floor box" is usually reserved for a box with a receptacle installed face up. You pose (possibly) a different dilemma, a "junction" box which would not have a device installed, does not have the same restrictions. The only "electrical" issue would be if it were subject to physical damage as determined by whoever inspected the work. Other than that, there may be safety implications.
Top
#214078 - 09/29/14 06:35 PM Re: Code for Junction Box mounted on Floor [Re: gfretwell]
dwhite Offline
New Member
Registered: 09/28/14
Posts: 4
Loc: IL
Thank you.
Top
#214079 - 09/29/14 06:39 PM Re: Code for Junction Box mounted on Floor [Re: Fiver]
dwhite Offline
New Member
Registered: 09/28/14
Posts: 4
Loc: IL
Yes - this is a junction box with conduit going over to the wall from the box. There is no receptacle. Based on the distances from the two walls, it seems like a safety hazard. The only reference I could find was that floor boxes had to be flush with the top of the floor, but maybe there are exceptions for J-boxes.
Top
#214080 - 09/29/14 07:08 PM Re: Code for Junction Box mounted on Floor [Re: dwhite]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
As 'Fiver' said, if it was inspected, the AHJ must have been OK with it.

It may be for a counter, desk, or some other item that is not installed.

As it sounds like it's in a corner, it probably is not considered a 'trip' hazard.

Just for info, what type of classroom,??




Edited by HotLine1 (09/29/14 07:10 PM)
_________________________
John
Top
#214083 - 09/29/14 09:57 PM Re: Code for Junction Box mounted on Floor [Re: dwhite]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Yup Fiver is right. I missed the "receptacles" in 317.17(C)
_________________________
Greg Fretwell
Top
#214120 - 10/06/14 08:34 PM Re: Code for Junction Box mounted on Floor [Re: HotLine1]
dwhite Offline
New Member
Registered: 09/28/14
Posts: 4
Loc: IL
It is in an elementary school classroom and has not yet been inspected. It is not for a counter or desk, and nothing will be installed over it. It is in a corner and, as mentioned above, it is about 16" from one wall and 8" from the other.
Top
#214121 - 10/07/14 07:44 AM Re: Code for Junction Box mounted on Floor [Re: dwhite]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
OK, if I was the inspector, 'Why is it there" and if no good reason..."Remove it"

Trip hazard, subject to physical damage, etc.

_________________________
John
Top
#214122 - 10/07/14 10:10 AM Re: Code for Junction Box mounted on Floor [Re: dwhite]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Does your state have a separate code for schools? In Florida they have the SREF codes that deal particularly with buildings in the school system. You might get something there,
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 81 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals