ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 353 guests, and 30 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#213773 07/15/14 05:36 PM
Joined: Apr 2013
Posts: 22
S
Member
I am working on a utility project. There are 2 Satec power meters wired in parallel across 2 bus breakers. The CT wiring is current flow into the meter terminals 1, 3 & 5 (correct for Satec's). The 2 meter current output terminals both wire to a 3rd meter, which is wired backwards (current in 2, 4 & 6, out 1, 3 & 5 wired in common to ground. Any ideas for the purpose of this.
Confused in New Jersey!

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2004
Posts: 1,273
T
Member
In all such cases, contact the tech rep for the device.

You do want a knowledgeable answer, no?

Voltages?
Amps?
wiring diagrams?
links?
problem?

Are these meter wired as a bridge?

Are you sure it's wired backwards?

Reactive power issues?





Tesla
Joined: Apr 2013
Posts: 22
S
Member
The Configuration is breaker and a half. Voltage is 69KV, CT's are 3000/5. The meters are part of a zone of protection, 2 breakers with an outgoing line between them.I have the 3-line and wiring diagrams. I contacted Satec and GE (there is also a GE D25 as part of the loop). Based on their responses, the devices are wired in reverse. I'm sending the 3-line to both GE and Satec. And yes, I don't want an "it's ok" answer. I want a knowledgeable answer so I understand how this works.
Greg

Joined: Apr 2013
Posts: 22
S
Member
I got an answer from the utility (one of their relay specialists) and the answer was so simple I felt dumb! The line is part of a switching station. It normally feeds another station, but could also be used as a feeder to our station. The devices are wired reversed to measure incoming power to our station.
Greg


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5