ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#213775 - 07/15/14 04:32 PM Minimum Bend Radius?
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
submitted by Gregory Madjeski:

Quote:
600v, 500kcmil cable termination.




Top
2017 / 2014 NEC & Related Books and Study Guides
#213777 - 07/15/14 07:44 PM Re: Minimum Bend Radius? [Re: Admin]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
OK, lets start a comment...

Judging by the insulation, and tinned conductor, this is an 'aged' installation.

Hard to tell from the pic, but the clearance from those extra long bolts??

Is the termination (clamp) rated for what appears to be parallel secondaries? Or is this unique engineering??

Is this a POCO transformer?? If so, then throw the NEC out!
_________________________
John
Top
#213779 - 07/16/14 02:58 PM Re: Minimum Bend Radius? [Re: Admin]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
Yes it's an older installation. The transformer is one of 3, single phase Allis-Chalmers "Curvacore" transformers and were used to step down 3 phase 4160V to 208/120V. I did a web search and couldn't find any info on them. All 3 were leaking oil and have been replaced.
Greg


Edited by sedesigner1 (07/16/14 02:59 PM)
Top
#213781 - 07/16/14 04:03 PM Re: Minimum Bend Radius? [Re: Admin]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Leaking oil? Did you, btw, try to soak a paper towel in the oil, then try to set it afire?

Old location .... oil that won't burn ... Hello, PCB's. Not really the sort of thing you simply toss in a dumpster or hose down the drain.
Top
#213784 - 07/16/14 05:03 PM Re: Minimum Bend Radius? [Re: Admin]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
They were tagged as PCB free, but I never touched it. There was a service tag on it at least. We were supposed to get an oil sample, but the sampling valve was so corroded we were afraid it would break. I see the same PCB free tags on oil filled utility breakers, but we're replacing those with SF6 dead tank breakers.
Top
#213785 - 07/16/14 05:21 PM Re: Minimum Bend Radius? [Re: Admin]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
OK, now we know 'customer owned', PCB free, a 'mat' setup, and old.

I had a few locations in Union County, NJ that I did demo and bringing the elec into the 20th century. Two locations were PCB issues,confirmed by my samples sent to a lab. The legal disposal was $$$ but necessary and a lot cheaper then dealing with a contamination issue. One of these sites had 'leakers' but thecontamination was limited to the concrete slab and 3' of soil.

Both of the above sites were replaced with POCO 2000KVA pad mounts and respective gear.

BTW, Welcome to ECN Forums from one of the 'Jersey Guys'!!
_________________________
John
Top
#213789 - 07/17/14 12:58 PM Re: Minimum Bend Radius? [Re: Admin]
sedesigner1 Offline
Member
Registered: 04/05/13
Posts: 22
Loc: NJ
Our "leakers" were on concrete so no oil went into soil, but the disposal fee was high (from what I heard). We also replaced the 4160 with a new 12.47KV service & POCO 300KVA 3 phase pad mount and gear. Some of the old stuff I see is almost beyond belief that somebody wasn't killed. Also, thanks for the welcome!
Greg
Top
#213795 - 07/17/14 06:47 PM Re: Minimum Bend Radius? [Re: Admin]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
You were lucky. Mine seeped thru what was an expansion joint.

I have to find time to look thru my old pics to see if I still have them.

PS:
Look here for a mat job...
http://www.electrical-contractor.net/for...t.html#comments


Edited by HotLine1 (07/17/14 06:52 PM)
_________________________
John
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals