ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#213392 04/21/14 10:03 AM
Joined: Feb 2002
Posts: 2,233
H
Member
I was asked a question and I have my own thoughts. I would like to hear yours. I hope I didn't post this question before, but here goes.

You have a nice 200 amp code compliant service. You want to add a generator so you install a nice big transfer switch with main breaker outside. So you change the service panel inside so that all of your neutrals are separated from the grounding conductors. Now the question:

The range was a 3 wire SEU wire. What happens to the neutral/ground conductor? Leave it with the neutrals? or the ground wires?

The same would occur with a dryer line if/when you used the old SEU wire for that. (Which around here was pretty popular years ago.)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The grounded wire in an old style dryer/range plug circuit using SEU is a neutral being used as a ground. You have created a violation when you put it on a sub panel, even on the 1993 code.

250-60(c) allows using the uninsulated conductor in SEU only if "the branch circuit originates at the service equipment"


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
OK Greg,

What happens if you want to install a transfer switch before the service and the whole house is finished? there is no way to run a new 3 wire feeder to the stove, then what are you suppose to do? Not install a generator? Or rip open finished walls in a house in order to run the proper cable? Is there a happy medium between the two choices?

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Not installing the generator leaves the existing range feed in place. How is that better than allowing existing equipment to be re-connected if it was acceptable at the time of original installation?

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Harold:
Sorry for not responding sooner.....BUT

The Rehab Code allows existing branch circuit wiring (range/dryer/etc) to 'remain 'as-is'.

The words are not verbatim but look on page 23-140, dated as revised 11/7/11.



John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
What John said wink

Generally if this was not in the scope of the new permit, you don't see it. Just like the lack of AFCIs or other things we can allow on the grandfather cause


If you did want a totally compliant new generator installation (all other things being OK;
You could choose to install a sub with transfer equipment for the emergency generator circuits (without the dryer)
or
You could use non-SDS transfer equipment where the neutral is not switched and the main bonding jumper stays in the current service disconnect.
or
You could extend the dryer SEU to a breaker in your new "main" panel. where the service disconnect and main bonding jumper resides.

There may be other solutions too but chances are nobody would ever care if you just left it alone. I do tend to agree that this has always been a potentially dangerous exception, even though we did not really pile up bodies and NFPA did well to get rid of it.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

Most transfer switches around here only switch the phase legs and the neutrals are almost always left tied together. So this is not a true separately derived system. Another question some EC's ask me is if they should leave the bare stranded neutral/ground on the neutral bar or the grounding bar. Since now the main service becomes a sub panel with a main breaker.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I am going to dig out my Soars grounding book. I think there are some diagrams there that are on point.
I remember Jim Pauley doing about 20 minutes on this is a grounding seminar.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

I think I have a Soares book around here somewhere.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5