BigB #211451 10/14/13 10:33 AM
Joined: May 2005
Posts: 984
Likes: 1
G
Member
Sounds like a job calling for a lot of cable lube.


Ghost307
BigB #211489 10/19/13 10:17 PM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Hi BigB,
I'm going out on a limb here, but instead of using one 90 degree bend, could you use 2 45° swept bends, to make the bends "easier"?
I'm not familiar with IMC fittings, but one thing I do know is aluminium is a real PITA to pull through conduit of any type.
My advice would be, if you are are in un-familiar territory, I would up-size your conduit, this will ensure that you don't run into problems with the pull.

I did my time with a guy that used to use the smallest conduit he was willing to quote, out on site, this made life a real nightmare, un-necessarily.
Take it from me, mate, bigger conduit makes the job SO much easier and less infuriating. grin

BigB #211805 11/16/13 06:15 PM
Joined: Jun 2004
Posts: 1,273
T
Member
Tuggers can be rented. Check with your tool factor.

If you were close by, I'd rent mine to you.


Tesla