A sump pump is being installed in a finished basement where the water heater, wash machine, and dryer will be located. Will this have to be on a AFCI breaker?? It will be bad if the breaker trips because of "nuisance" tripping while they are on vacation, and the water heater or water pipes break:( Of course this could possibly happen in any scenario, but what does the code say?? thanks...
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I would leave an area or room around the sump pump "unfinished" but it would still need a GFCI. In my house, it would be a regular circuit and "come and get me copper"
Greg Fretwell
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
Greg, even if is a single recpt. so that nothing else can be plugged in, it's required to be GFCI?? Thanks
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
There is no exception regarding a single receptacle,
A GF trip is not 'good' for an active sump pump, but the possibility of a shock hazard has priority.
John
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
another question related to this same job. When a ceiling is dropped in a full basement, do the joist still have to be bored out for the wires? Sorry not up to digging in the code this morning, hitting on about 4 out of 8 cylinders:) Thanks on the reply about the GFI. I didn't see it in time...
Last edited by sparkync; 07/20/13 01:25 PM.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
sparkync:
From the '11 NEC: "(C) Cables Through Spaces Behind Panels Designed to Allow Access. Cables or raceway-type wiring methods, installed behind panels designed to allow access, shall be supported according to their applicable articles. '
That said, there is nothing within Art 334 that says you have to drill.
However, your local AHJ may have another opinion. The "physical damage" can be subjective.
John
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
thanks John, I don't think (in my opinion) that it is going to subject to physical damage above ceiling tile... That's in my opinion hope the AHJ has the same opinion
|
|
|