ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 335 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#210624 07/14/13 04:38 PM
Joined: Apr 2012
Posts: 7
S
New Member
When referring to with jacket or without jacket, is this bare copper or with insulation for the purpose of the number of conductors in a trade sized conduit?

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
USEI conductors are jacketed. Single conductor wire used to have a cloth jacket.

On a similar topic, Table 6 is for stranded conductors. Solid conductors are a little smaller but you can always use Table 6. It's the worst-case measurement.

When you need to push it, you can use the manufacturers measurements and when you really need to push it, you can measure the wire and the conduit.

Here are some tables using the manufacturer's specs: http://www.codemath.com/cgi-bin/Run.pl?script=FillTbls

Joined: Dec 2007
Posts: 35
H
Member
i'll go one better. have'nt you heard the question, how many wires can you pull into a conduit? answer is, how big is the gorilla on the fishtape. had to throw that one out there.

Joined: Jun 2006
Posts: 613
M
Member
Jacket is another coating not related to insulation. Loomex has 2 insulated conductors, a bare bond wire and all enclosed in a jacket of plastic. Once it was woven cloth.
Some single conductor cables are jacketed and insulated. I have seen these used for street lighting. The jacket permits direct earth burial.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5