Joined: Jun 2012
Posts: 75
Member
Hi,
Does article 110.26 (A)(1) apply to the disconnect for the condenser unit?

or would this fall under 440.14 only required to be in sight?

I have two units with the disco mounted behind the units less than 2 feet away from the condenser..

I am thinking you need width of equipment or 30" and mounted to the left or right.

thanks

for any replies.

greg


Don't drive and TEXT! Drive now TALK LATER!
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
It is unclear.
Most AHJs do require working space in front of the condenser disconnect. The strange thing is the same guys don't seem to care about the air handler, that might be in a closet or up in the attic where is no way you can push Jim Pauley's mythical refrigerator box up to the disconnect (a rough idea of what working space looks like that he uses in his road show).


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
If we are talking resi, clearance issues on new construction arise when 'who is there first'. When the EC is doing trim out for finals, he mounts the discos at the location. The CUs are dropped after, and sometimes the disco is behind them, or the tall units block the disco.

When the AC line set is in & charged, guess who has to move what??

Replacement CUs usually are OK. Best comment I can add is each job has to be treated individually.

Commercial RTUs are usually no issue.

Do we live in a perfect world, No.


John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The world is not even perfect at my house We put in a mini split and I wanted the condenser set near the existing one but about 3' away so I would maintain my 30" in front of the grouped disconnects with a little wiggle room to spare. I even put the pad in with the center that far away. The <expletive deleted> installer put it near the close edge of the pad!!! I ended up with about 28" as far as we could push it without running another line set.
Fortunately the inspector left his yard stick in the truck.



Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
In areas that were inundated by "Sandy":

It is getting real interesting with the attempts to comply with elevation heights above the proposed new flood levels.

Replacement CUs range from the 'I don't care it staying on the grade' to 3'-8' above grade.



John
Joined: Jun 2012
Posts: 75
Member
Thank you guys for the comments..very insightful..

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Putting A/C condensers (water heaters etc) above the FEMA flood plane has been standard here for years if the finished floor of the home is FEMA compliant.
You see blocked up platforms under the condenser or water heaters in garages that are below the FEMA level.

If the house is grandfathered below FEMA, they usually ignore the water heater and AC.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
John,

Do you have many Cu's up in the air on the second floor? I have them here in my town. Nothing sillier than looking out a second floor window and seeing a tiny deck with an HVAC unit sitting on it.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Is that an indication of where FEMA says the flood plane is?
We see that at the beach where they have to build piling houses. These days the FF is about 14 feet off the sand and that is up hill from the water. They are usually 10'-12' higher than the road out front.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

In one of the towns I inspect, the town gave people permission to raise their houses as long as it was the height that was governed by FEMA. The heights were different in several parts of town. Needless to say, the closer you were to the river, the higher the flood plane was. They will even allow you to build a new house in the flood plane, but there is no basement and no walls on the first floor. The water has to be allowed to flow in, under, and around the house. So all of your utility services enter in on the 2nd floor.

The water and sewer comes up out of the ground and is wrapped around with all sorts of protection from cold, inside of a hollow column.