1 members (Scott35), 131 guests, and 11 robots.
#210161 05/30/13 05:40 PM
Is there a article in the code that requires a slope of 3% oriented to the manhole? Or does it cover that at all?
Please quote article if possible.
Thank you.
Greg
Don't drive and TEXT! Drive now TALK LATER!
akmaster #210163 05/30/13 05:58 PM
I believe article 310 covers manholes..
akmaster #210173 05/31/13 08:03 PM
Is the manhole owned by a utility company or privately owned? Is this a service wire, feeder wire from 1 building to another? Maybe the guys need a little more info.
akmaster #210175 05/31/13 08:20 PM
It is one of many manholes on an ethanol project...it will contain Medium voltage cables (4160) fiber and control and DC circuits..the are 8'x 8'x8'. They have a base and a top...
the specs call for a 0.3% slope TOWARDS the manhole..
I did not find that requirement anywhere in the code..
It seems they will need racks inside to rack the cables as well..
Thanks,
Greg
akmaster #210176 05/31/13 09:24 PM
Toward the manhole? Is this also the storm drain system?
akmaster #210182 06/01/13 02:36 PM
Greg,
Check sec. 110 V of the NEC, that talks about manholes and their construction also sec. 490 talks about voltage over 600. You also might have to refer to the National Safety Code. Most utilities follow those rules. I might have an old NESC book around, I would have to look.
akmaster #210186 06/01/13 04:39 PM
This may say something: From '08 Handbook:
"110.70 General.
Electrical enclosures intended for personnel entry and specifically fabricated for this purpose shall be of sufficient size to provide safe work space about electrical equipment with live parts that is likely to require examination, adjustment, servicing, or maintenance while energized. Such enclosures shall have sufficient size to permit ready installation or withdrawal of the conductors employed without damage to the conductors or to their insulation. They shall comply with the provisions of this part.
Exception: Where electrical enclosures covered by Part V of this article are part of an industrial wiring system operating under conditions of maintenance and supervision that ensure that only qualified persons monitor and supervise the system, they shall be permitted to be designed and installed in accordance with appropriate engineering practice. If required by the authority having jurisdiction, design" (documentation may be required)
akmaster #210208 06/03/13 02:17 PM
Thanks for the replies. @ Greg...yes towards the manhole...
@hotline...thanks I will take a look...
I can not find any requirement regarding slope of 0.3 percent towards the manhole for conduits...
does this include the whole run from man hole to man hole?
regards
Greg
akmaster #210230 06/04/13 02:15 PM
Another question: Is it not a requirement that manholes with high voltage are required to have the cover labeled "DANGER HIGH VOLTAGE"?
Thanks
GW
akmaster #210231 06/04/13 02:25 PM
One more...Does the Manhole cover have to be grounded?
