Electricians revenge
1 members (Scott35), 180 guests, and 10 robots.
#20957 01/24/03 09:52 PM
Gwz Offline OP
What are some of the typical HyPot voltages and time for 1/C 5KV and 15KV cables with shielding ?
Is their a 'Rule of Thumb '?
#20958 01/24/03 11:52 PM
2 times the rated voltage times 75% for 1 minute....record the reading....take another reading for 10 minutes...record that reading.
divide the first reading into the second reading....EASA recommends the answer should be 2.0 or higher.....but, 1.5 is prolly o.k.
#20959 01/25/03 02:45 AM
There are different levels for new versus maintenance testing, and 100% or 133% insulation.
One chart is http://www.kerite.com/catalog/catalogfiles/DC_field_testing_power.htm
Be Careful. You’re charging up fairly big capacitor(s) in the process. The test-set instruction manual is a good reference.
[This message has been edited by Bjarney (edited 01-25-2003).]
