BigB Offline OP
Member
I am pretty sure infrared heaters installed on outdoor patios must be figured at 125% and included on residential load calcs, is this correct?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
They get computed at 100% on the load calc but the branch circuit gets sized at 125%.


Greg Fretwell
Joined: Mar 2004
Posts: 814
B
BigB Offline OP
Member
OK thanks Greg

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Depending on which method you use the bottom line may not end up being the whole load added with the heaters but the 100% is what you plug into the calculation.


Greg Fretwell