ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Mar 2004
Posts: 814
B
BigB Offline OP
Member
There is a concern on an existing installation where the meter and outdoor load center are approximately 7 feet from the inside wall of an in ground pool. Looking thru 680 I see no violation, not even a requirement to include it in the equipotential bonding as it is not within 5 feet of the inside wall. Am I correct?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I think you are right but look up. Where is the service drop?


Greg Fretwell
Joined: Mar 2004
Posts: 814
B
BigB Offline OP
Member
Originally Posted by gfretwell
I think you are right but look up. Where is the service drop?


The service conductors are piped across the roof for 25 feet then there is a 90 up with a weatherhead. Adjacent to this weatherhead there is a service mast fastened to the building to support the overhead, keeping it 25' from the water. It is not pretty.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


Greg Fretwell
Joined: Mar 2004
Posts: 814
B
BigB Offline OP
Member
Originally Posted by gfretwell
It sounds legal tho... sometimes the law ain't pretty wink

Was any consideration given to raceways on a roof? (derating)


I doubt it since my area just started enforcing derating for ambient last year, and this installation is at least 30 years old. This brings up something I have been wondering about, when de-rating residential service conductors would you start with the ampacities listed in table 310.15(B)(6)?

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
That is why I was curious.
310.15(B)(2)(c) refers you to 310.16
I am not sure what you do with (B)(6) service feeders. I was wondering what size they ended up with.


Greg Fretwell