The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Recent Posts
Re: Habitable room?
by gfretwell
Today at 12:37 AM
Proper installation of PVC conduit
by gfretwell
Today at 12:19 AM
Make sure to get permits
by schenimann
Yesterday at 10:40 PM
Bonding Metal Piping 250.104 (B)
by schenimann
Yesterday at 10:13 PM
Outdoor receptacles
by twh
Yesterday at 09:48 PM
New in the Gallery:
Another Aussie style crawfoot outlet
Shout Box

Top Posters (30 Days)
gfretwell 82
HotLine1 63
harold endean 46
akmaster 39
sparkync 20
Who's Online
3 registered (shortcircuit, Buck_Nekid, Texas_Ranger), 66 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 3 of 3 < 1 2 3
Topic Options
Rate This Topic
#206223 - 06/07/12 07:14 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7875
Loc: Estero,Fl,usa
It is interesting that depeding on which document you look at for this device it might be restricted to NM-b only or any copper NM, it might be restricted to modular homes or in any dwelling. They seem to have had several changes of heart and still have documents around to allow the various uses.
_________________________
Greg Fretwell

Top
2011 NEC & Related Books and Study Guides
#206227 - 06/07/12 07:50 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 5623
Loc: Brick, NJ USA
A thought that popped into my head today: Wind the clock back to the late '70s doing maintenance/rehab type work.

easy job, replace hall light fixtures in 3 & 4 story multi-family bldgs. Old fixtures from the '50s; old tight spiral steel BX, pancake boxes with old gas nipples still there. Three wire (two circuits), two lamp surface mounted fixture, 100 watt bulbs.

Crumble disaster no matter how careful you were, down to the bare conductors. Boss says.."cut it back to good wire"!
Heck, it was luck IF there was any slack. A BX version of that TYCO gizmo would have saved countless hours.

Old, past sins committed ('buried boxes') are well past the statute of limitations.
_________________________
John

Top
#206229 - 06/07/12 08:43 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7875
Loc: Estero,Fl,usa
Quote:
Old, past sins committed ('buried boxes') are well past the statute of limitations.


Yup, only the installer and the fire department will ever know wink
_________________________
Greg Fretwell

Top
#206574 - 07/17/12 05:35 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
mikesh Offline
Member

Registered: 06/07/06
Posts: 607
Loc: Victoria, BC, Canada
How much 90 wire do you need before splicing on to 60 degree wire? This is not well defined and my answer is entirly inferred from other sources. Almost all product standards use 1.2 meters of wire as the default length to dissipate heat introduced at 1 end of the wire. Breaker tests use 4 feet. pot lights only use about 18 inches of 110 degree wire to get to the external JB where 90c wire is required.
When inspecting older homes I regualry reject new lights on old wiring. except for luminaires with a canopy and pendant most luminaires now have a 90c minimum temperature rating. so where new high temperature fixtures are installed on old 60c wiring it is pretty common to see no insulation on the wires if they are even touched. by splicing in 4 feet of wire between the old box and new luminaire we generally avoid this issue but the old JB is all to often in the exact location they want the new JB and light to be mounted. Not too hard if you can lift the box from the attic but the extension can be very hard to accomplish. It is usually best to find a luminaire that can be connected to 60c wire.

Top
#206575 - 07/17/12 05:44 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
patrick1 Offline
Member

Registered: 12/17/06
Posts: 18
Loc: bensenville
I have the same perspective also mikesh, with regard to older wiring and luminaire requirements,..there is always some way to get it done right or to the minimum requirements, it just takes a little more T&M.

Top
#206576 - 07/17/12 09:09 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4864
Loc: Blue Collar Country
How did this thread get this long without me? laugh

90 degree? Heck, I frequently see a 105 degree requirement with the Ruud HID lights I use.

As I see it, the requirement ends as soon as you leave the enclosure. In practice, this means either a box on the opposite side of the wall, or a splice where the mounting meets the pole.

This has to be a requirement completely ignored by the trade, as the folks at Graybar have absolutely no idea what wire to supply. Inquiries typically get an answer involving a couple thousands feet of wire, with a price of $5/ft.

It seems that the electrical parts houses are completely ignorant of the high-temp appliance wire sold at the local hardware store or appliance repair shop. This is the stuff covered with woven fiberglass. 0.75/ft, cut to length, any color you want.

Top
#206577 - 07/17/12 11:54 PM Re: 90 C RATED TERMINATIONS AT LUMINAIRE TERMINATIONS [Re: patrick1]
Tesla Offline
Member

Registered: 06/16/04
Posts: 951
Loc: Sacramento, CA
John..

MTW wire carries a 105ºC rating...

The last time i looked my THHN/THWN-2 also carried an MTW rating...

Look for this on #14 stranded tap wires.
_________________________
Tesla

Top