ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#206346 06/17/12 09:41 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Found this on a re-inspection. No GFI, no cover on receptacle, open KOs...

[Linked Image]

Last edited by HotLine1; 06/17/12 09:41 PM.

John
Joined: Mar 2008
Posts: 144
Member
Shower of sparks wink


-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH
Joined: Aug 2006
Posts: 81
A
Member
Is the 45 going into the box a chrome shower arm?

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Yes sir! That it is!


John
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I never thought of that ... a shower arm .... well, you've got to admire his resourcefullness!

Now ... let's open our minds a bit, and ask "what's REALLY wrong with this installation?"

That is, let's overlook all the 'pro forma' things like the lack of a UL sticker. Instead, let's pretend we're standing in the lab at UL, and this kludge comes in to be evaluated for listing.

What points would you focus on? Could something like this pass muster?

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
1/2" IMC/RGC & a bender with some talent could rectify this.

"It works"?? Yes, is there a equip ground path? Yes! Even thru the plumbing copper fitting. Could UL or any RTL be OK with this? Perhaps. But....paying the $$$$$ for evaluation IMHO is not cost effective. (See opening line of this post)



John
Joined: Jul 2004
Posts: 787
L
Member
Would the surface finish of the interior of the pipe and fittings be a cause for concern? Specifically the edges of the threaded portions.

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Judging on the workmanship...probably NM in the pipe.



John
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Hotline, I wasn't referring to a one-off 'field evaluation.' I was asking ... what's really wrong here?

I'm a bit disappointed in the lack of thoughtful replies. Maybe I should give it a try ...

Code already requires the pipe ends to b free of burrs and sharp edges.

Let's look at that shower arm as if it were any other piece of conduit:
OK, I see threads. Would it pass muster as IMC? After all, there are strength and wall thickness requirements for IMC.
There's also a minimum bending radius. Does this comply?
One difference between plumbing pipe and electrical pipe is that the ASTM standard specifies that the inside of electrical pipe be 'smooth.' In practice, this means that the lengthwise ridge formed when the pipe was welded together has been removed. What does the inside look like here?
I expect the plating does give enough corrosion protection.

What about copper pipe / tubing? Well, if you look at the relevand product standards, there's always room for alternative materials of similar strength. Maybe one of the copper tubing grades would pass muster as EMT.

A problem arises with the fittings, as code tells us we cannot rely upon solder alone for our connections. Now, if they used an old-style 'dimpler' together with solder, they'd be good to go.

Let's look at that Bell box. First off, what's to keep the connection from coming loose? I'd want to see a locknut there.
Just as important, code requires the box to be supported by at least two conduits, where conduitprovides the support. I only see one.

Open KO's, etc., are issues that would apply to any installation.

Joined: Feb 2002
Posts: 2,233
H
Member
Gee John,


A plumbing shower arm for electrical work. What's wrong with that? Now your getting picky! smile

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5