ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 520 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: May 2012
Posts: 13
S
sidmuer Offline OP
Member
Hello,
If I have a 60 AMP panel or device on 60 AMP breaker, and the wires are 2/0 RW90XLPE feeding the panel or device, do I size the ground for panel or bond for device by the wire size or by the panel rating/breaker size or, if it's a device, by the breaker size of that device?

I know for a panel, min size for ground is #6. So for the 60 AMP panel, I'd need at least that. But that is still well below the size needed to ground 2/0 rated wire.
Or a bond for 2/0 rated wire running from a 60 AMP breaker to a device.

I just don't know if I am supposed to size grounding or bonding by the size of wire ran or the breaker it is on. I would hope by the breaker size.

Joined: Aug 2002
Posts: 402
J
Member
If you use table 16 it is based on the 'largest ungrounded conductor in the circuit..." not on the panel size or overcurrent protection.

Last edited by jdevlin; 05/31/12 10:30 AM.

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5