1 members (Scott35), 381 guests, and 13 robots.
sidmuer Offline OP
Hello,
If I have a 60 AMP panel or device on 60 AMP breaker, and the wires are 2/0 RW90XLPE feeding the panel or device, do I size the ground for panel or bond for device by the wire size or by the panel rating/breaker size or, if it's a device, by the breaker size of that device?
I know for a panel, min size for ground is #6. So for the 60 AMP panel, I'd need at least that. But that is still well below the size needed to ground 2/0 rated wire.
Or a bond for 2/0 rated wire running from a 60 AMP breaker to a device.
I just don't know if I am supposed to size grounding or bonding by the size of wire ran or the breaker it is on. I would hope by the breaker size.
If you use table 16 it is based on the 'largest ungrounded conductor in the circuit..." not on the panel size or overcurrent protection.