I have a situation where I need to power a intermittent single phase large load with a three phase transformer so I will not be using one leg. Its short term hook up for two to three years at best so I do not want to buy a transformer ($$$$$) when I have a 3 phase dry transformer collecting dust of sufficent size. I have not come up on this type of config before so I have my conserns. Such as
*Would it be kosher to wire and tap only two of the three coils?
*if not, what issues would I have if I were to wire the high side 3 phase and only use two legs where the amperage in theory be upto 100 amps, 90 more realistically and only intermittenly?
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
I've seen this done over the years, as having 3 phase wired as normal, secondaries going to a disconnect/panel, and single phase load being connected.
Can't say I heard of any problems.
IMHO, as long as the xfr is of sufficient KVA, you should be OK. Efficiency? May be an issue.
Scott....jump in here please!
John
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
Does the transformer have each end of the secondaries available for separate connection? If so, you could hook them up in a "dog leg" connection to get single phase out of a three phase source.
It is the same method that is used on three phase generators when they need to supply single phase loads.
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
I timed out while editting. Use the following "Scott" drawing. 12 lead generator drawings Basically it is a open delta where Phases A & B are connected in opposing series and Phase C is connected in aiding series to the combined A & B. The output "L1"is connected to the free end of A, the "neutral" is the connection between B & C, and "L2" is the free end of C. The connection between A & B is not used. This limits the unit's maximum power to 2/3 of full rating but is does load the 3 phase input equally. Larry C
|
|
|
|
Joined: Jul 2007
Posts: 1,335
OP
Member
|
I am not sure if it's a 12 wire transformer or not. I currently do not have access to it.
Larry, I think the the 12 lead generator link is hinky. It takes me to some web site. I do have schems of generators and I didn't thInk of looking at it from your perspective.
Thanx for everyone's input
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Jul 2004
Posts: 9,923 Likes: 32
Member
|
Maybe I am missing something but why not terminate in a 3 pole disconnect and feed a single phase panel from there or just use a 3p panel with one 2 pole breaker plugged into it.
The transformer won't care.
Greg Fretwell
|
|
|
|
Joined: Jul 2007
Posts: 1,335
OP
Member
|
That is what I'm planning to do. By maxing two of three legs while having nothing on the third leg, I dont know such an unbalance would cause any issues for the transformer and or the circuits or not. That would be a rather expensive smoke test if overlooked something
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Jul 2004
Posts: 787
Member
|
The link is hinky because address got changed from electrical-contractor .... to electrical.contractor ....
The link is supposed to go to the technical drawings on this site.
Larry
|
|
|
|
Joined: Jul 2007
Posts: 1,335
OP
Member
|
Ah ha! That did it. Thanx Larry.