The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
2 registered (sparkyinak, OverZealous), 98 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#205066 - 01/29/12 10:02 PM Re: 250.32(B)(1) 2005 NEC [Re: BigB]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
There is quite a bit of current flowing through the ground, particularly in wye distribution.
_________________________
Greg Fretwell

Top
#205129 - 01/31/12 09:07 PM Re: 250.32(B)(1) 2005 NEC [Re: BigB]
pdh Offline
Member

Registered: 01/20/05
Posts: 347
I always insist on fiber optic between buildings, for the data connections.

But there has for a long time been issues with shared metallic paths between buildings with separate services (e.g. a neighborhood of homes on the same metal water pipe, cable TV coax, etc). If one of them loses neutral on the service drop, guess what gets to carry the difference (and all along it was carrying a fraction of it, anyway). I'd rather my water and gas come in on plastic piping, and the phone/TV/internet come in by fiber or RF, just to avoid those issues. Eventually, I'll get it arranged that way (it was hard enough just getting the cable company to properly ground their stuff).

Here's a fun one to consider:

Utility service drop comes to the house. A whole house (25kVA or more) generator is inside the separate detached (and powered) garage. How can you wire up so the house is powered by the generator, and not only comply with 250.32(B)(1) but also be sure the proper transfer(s) exists.

Top
#205133 - 01/31/12 09:32 PM Re: 250.32(B)(1) 2005 NEC [Re: BigB]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
You are going to have problems any time you put a generator on the other side of the garage unless you feed it all the way back to the service.
_________________________
Greg Fretwell

Top
#205137 - 02/01/12 06:36 AM Re: 250.32(B)(1) 2005 NEC [Re: gfretwell]
pdh Offline
Member

Registered: 01/20/05
Posts: 347
No matter how you do it, I don't see any way to avoid TWO runs. There is just no safe way to share a single run and switch directions on it. But how to avoid grounding loops in that? Either the generator is isolated from the garage completely, or you have two transfer switches (with neutral transfer). But does it have a single EGC?

Just stuff to think about (when you have time to think about weird things).

Top
#205143 - 02/01/12 11:31 AM Re: 250.32(B)(1) 2005 NEC [Re: BigB]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
You never switch the EGC and it can be tied to earth as many times as you want. The only issue is where it gets bonded to the neutral.

I am still not sure how you could coordinate two transfer switches in a compliant way. You really need to bring the generator feed back to the service entrance.
_________________________
Greg Fretwell

Top
#205186 - 02/04/12 09:55 AM Re: 250.32(B)(1) 2005 NEC [Re: BigB]
pdh Offline
Member

Registered: 01/20/05
Posts: 347
I certainly would not switch the EGC. I'm just wondering if there might be issues with having 2 or more parallel EGCs. For example, existing conduit is filled with power from house to garage. If adding the generator at garage to feed to the house (whether generator to garage power takes it directly at the garage, or lets it loop first through the house), does one need to abandon/replace the existing conduit, so that the new conductors, as well as the old (though possibly replaced to physically new), can both be run immediately adjacent to a single common EGC. Or can they be separate with duplicate EGC which might be interconnected on both ends forming its own loop (but in any case, any fault currents would certainly run parallel in both conduits if set up like that ... plus over the cable TV coax, wtx, so that's not really a solved issue)?

It seems to me (I didn't try to look this up) the correct way is one conduit big enough for all this, 3 conductors for house to garage, 3 conductors for garage/generator to house, and 1 EGC (change 3 to 4 for 3ph where that might happen to be).

Also, it seems to me that if multiple EGC connected together at each end is not a good thing, then letting TV coax shield be wired the same way is also not a good thing.


Edited by pdh (02/04/12 09:56 AM)
Edit Reason: Also, ...

Top
#205189 - 02/04/12 12:14 PM Re: 250.32(B)(1) 2005 NEC [Re: BigB]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
We have multiple EGCs all the time. Every time you pull a green wire in a pipe you have a parallel EGC and the HCF rules even require it.
As far as the code is concerned ground is ground and the more the better. If we have multiple circuits passing through a J box, don't we bond all of the EGCs together? We reground the EGC pretty much any time we can (generator frames, additional buildings etc).

We do get concerned with the neutral.
_________________________
Greg Fretwell

Top