Several years back, I posted an Image of an Ideal Red Wirenut, which had extensive Heat-Related damage.
The Wirenut was found in a 4s Box, during the Demo Phase of a Tenant Improvement (T.I.) Project.
Several others were found as well; a few were so Heat Damaged, that they disintegrated upon touch.
The culprit:
Poor Workmanship!!!It was obvious that the Terminations were done by more than One Person... most likely there were Three People doing the Makeup on these Ceiling Boxes.
The Boxes with "Poor Workmanship" comprised of less than 20%, had no Writing on the Covers (to indicate Panel / Circuits + Voltage), were only the Lighting Circuits (277V), and were the only Terminations where no Pre-Twisting was performed.
The Pre-Twisting inclusion is simply an observation of bulk Terminations, not an indication of Termination Failure where not performed, as I have seen many undamaged non Pre-Twisted Terminations.
Points to ponder:
1: The Service Capacity which these Lighting Circuits were fed from, was 4,000 Amps - 480Y/277V 3 Phase 4 Wire; so the Service Disconnect (Main Circuit Breaker in this case) included GFPE (Ground Fault Protection for Equipment).
2: The settings were dialed in for most restrictive / highest sensitivity.
3: Although the GFPE does not directly scan for Series Arcs, there was evidence in some of the effected 4s Boxes, showing L-G Arcing.
To me, the Termination issues discovered on this Project are very rare scenarios. I had been in the field for at least 24 Years when discovering the Bad Terminations. Prior to this I had uncovered only a few (no more than 5) such situations - only there was a single Termination issue (only One Wirenut in One Box total), and the Wirenut was either an obviously over-used Ideal, Scotchlock, or something in the "El-Cheapo" line...
My Conclusions:
a: Termination Failure is directly related to the experience of the Person performing the task,
b: The Workmanship placed on any installation, may vary with a Person - per the situation involved (i.e.: bad day = poor makeup),
c: The Wirenuts in this case were damaged from excessive Heat, caused by drawing 100% LCL Current through the internal spring mechanism of the Wirenut,
d: Little, if any, Series Arcing was experienced in the Wirenut,
e: The only way any Protective Device would react to these scenarios, is when a Bolted Ground Fault occurred (Wirenut Spring made contact with the Metallic Enclosure of an Outlet / Junction Box),
f: This is not a Brand-Specific issue. All brands and types of Solderless Terminations have the potential to fail this way, due to Poor Workmanship.
Just my 2¢

-- Scott