#204895 - 01/19/12 03:52 PM
Bonding size for CSST
|
Member
Registered: 08/15/05
Posts: 210
Loc: Waterford, MI, USA
|
Hey guys...
So what I have here is bonding of Corrugated Stainless Steel Tubing (gas line manifold) . I say a #8 solid is ok. Inspector comes in and says the building inspector wants a #6.
Not sure if I agree. Electrical inspector said to contact the building inspector and see about getting that overturned.
Can you guys give me your thoughts on this and maybe an angle I can go forward with when talking to the building inspector?
On a sided note; I would usually just change it out to the #6, but we have already done 3 houses this way and have many more to do. Its cost effective to get this straight. This is also in the beautiful city of Detroit, where copper gets stolen all the time. So the less copper the better.
|
|
Top
|
|
|
|
#204896 - 01/19/12 03:59 PM
Re: Bonding size for CSST
[Re: Trick440]
|
Member
Registered: 08/15/05
Posts: 210
Loc: Waterford, MI, USA
|
I should really use the search feature before posting. It looks like I do need to run a #6.
"CSST Bonding – What is Required? There is confusion on what is going on with CSST, flexible gas piping, since the manufacturers have been sending out revised installation instructions with their material. The revisions were a result of a lawsuit in which the court stated that the manufacturers must provide a means to protect the CSST from lightning. The revised instructions are requiring that the CSST be bonded to the grounding electrode conductor. The installation instruction requirements are not in compliance with the currently adopted codes. The code requires that CSST be bonded, not grounded or used as a grounding electrode. Section 250.104(B) of the 2005 National Electrical Code (NEC) states that the equipment grounding conductor is permitted to serve as the bonding means for the gas piping. Otherwise, bonding is required to be from the CSST connector coupling to the water piping. The size of the bonding conductor is based on the rating of the circuit likely to energize the piping system. Table 250.122 in the 2005 NEC provides the conductor size based on the ampacity of the circuit. For example, if there is a gas heater with no electric at all to it and the service to the dwelling is 200 amperes, Table 250.122 states that 6 AWG copper or 4 AWG aluminum is required for the bonding conductor. The clamps installed on the water and CSST pipes must be listed and labeled in accordance with Section 250.8 of the 2005 NEC. The clamps may be a dissimilar metal, provided they are approved and listed for the use. In conclusion, no additional bonding is required where there is electric to any gas appliance, since Section 250.104(B) of the 2005 NEC permits the equipment grounding conductor to serve as the bonding means for a"(gas piping system.
Discuss?
Edited by Trick440 (01/19/12 04:00 PM)
|
|
Top
|
|
|
|
#204911 - 01/20/12 08:28 PM
Re: Bonding size for CSST
[Re: Trick440]
|
New Member
Registered: 09/24/04
Posts: 6
Loc: Carolina
|
Yeah, I'm surprised how smoothly that requirement was foisted upon us. It irks me that a gas pipe manufacturer can rush a product to market before adequate R&D, and then when it fails, force another trade to fix their problem.
But the end may be in sight? A mechanical contractor told me a coupla weeks ago that they are going to stop making the yellow stuff.
Since CSST bonding is not addressed by the NEC, to get the specifics, here is what is required in our area: "It shall be the responsibility of the Mechanical contractor to provide the electrical contractor and the electrical inspector the installation instructions for each and every CSST piping installation."
|
|
Top
|
|
|
|
#204914 - 01/21/12 10:21 AM
Re: Bonding size for CSST
[Re: Trick440]
|
Member
Registered: 11/27/07
Posts: 726
Loc: MA, USA
|
I think maybe this is similar to the situation for smoke alarms and smoke detectors. The NEC doesn’t specifically require them, but our state building code does and also specifies their location as well as the type of sensors used. Seems to be basically the same thing now with CSST. IMO, other than what’s addressed in 250.104[B], it’s not really an NEC issue, so much as a building code and plumbing code issue. Here we just run a #6 CU bonding conductor to the gas piping manifold or location where the gas piping changes over from black iron to CSST. Our state actually banned using CSST for a short time until manufactures addressed the problem of lightning strike damage, so this seems to be the solution the manufactures came up with, and what the state building and plumbing code Dept’s accepted.
|
|
Top
|
|
|
|
#204963 - 01/25/12 01:18 PM
Re: Bonding size for CSST
[Re: Trick440]
|
Member
Registered: 04/03/02
Posts: 4792
Loc: Brick, NJ USA
|
I guess it's better late than never... I finally got around to getting this from our Plumbing Inspector, who got this at a recent seminar.
From the IFGC (International Fuel Gas Code, 2009) 310.1.1 CSST. CSST gas piping systems shall be bonded to the electrical service grounding electrode system at the point where the gas service enters the building. The bonding jumper shall not be smaller than 6AWG copper wire or equivalent.
That is probably where the inspector in the OP obtained the #6 size from.
Jurisdiction here (NJ) is the Electrical Inspector, and a NJ Lic EC is required to do the install and obtain the permit for same.
_________________________
John
|
|
Top
|
|
|
|
#204987 - 01/26/12 01:45 PM
Re: Bonding size for CSST
[Re: Trick440]
|
Member
Registered: 04/03/02
Posts: 4792
Loc: Brick, NJ USA
|
Reno:
I'm 100% with ya on this, but I have no choice as this is written.
We (NJ) used to use "gas piping is bonded via the EGC in the appliance" (My words, not the way it was written) This was a subject of many heated debates.
Basically, now, IF CSST is installed the gas pipe installer is required to have a Lic EC pull a permit for the bonding/grounding install, and have that inspected by electrical inspector. To date...I have seen zero.
_________________________
John
|
|
Top
|
|
|
|
#204995 - 01/27/12 10:10 AM
Re: Bonding size for CSST
[Re: HotLine1]
|
Member
Registered: 11/27/07
Posts: 726
Loc: MA, USA
|
I see that Mike Holt sent out a newsletter today with a link to yet another article that outlines the problem of lightning strikes and the resulting fires that seems to have plagued CSST since its beginning. In the article they mention that they have seen some problems even where the gas tubing was properly bonded, so that doesn’t sound too promising. CSST Article
|
|
Top
|
|
|
|
#204996 - 01/27/12 10:46 AM
Re: Bonding size for CSST
[Re: Trick440]
|
Member
Registered: 07/20/04
Posts: 7060
Loc: Estero,Fl,usa
|
I can't get past the ad.
Maybe the answer is to parallel the CST with a bonding wire, connected at each joint, to keep everything at the same potential from end to end. I do not know of any code that says that tho.
_________________________