The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
05/23/12 06:34 PM
450.3(C)
by Tesla
05/23/12 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
05/23/12 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (OverZealous), 94 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204740 - 01/04/12 12:45 PM temporary roll up generator
dbravo Offline
Member

Registered: 05/04/10
Posts: 23
Loc: NY, USA
I have to replace an existing unit substation that supports a 50,000 sf building. During construction, I am proposing a temporary roll up generator with a termination cabinet between the generator and existing dist. equipment to provide temporary electrical services during construction. The generator will feed a 800A MCB dist. panel. I understand per Art 590 (2011) a temporary service must be installed as a permanent installation er Art 230.

Are there any concerns that I should be aware of? I feel like I am missing something?

Thanks in advance.

Top
#204742 - 01/04/12 01:00 PM Re: temporary roll up generator [Re: dbravo]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
dbravo:

IMHO, you should refer to 590.2 (b), check with the local AHJ regarding your proposed temp install.

Conforming with 230 part 1 thru 7 requirements, should not pose any issues, based on what you described above.

MOCP at the gen, feeder to your MDP and branch circuits feeding your loads.