Joined: Apr 2002
Posts: 32
S
sudsy4 Offline OP
Member
Any suggestions on how to tap 4 panels (350MCM each) from 3 parrallel 600MCM feeders in a gutter?


Bill
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
'Polaris' type terminations; 600 to 350 range, 7 barrel, or 8 to be safe.


John
Joined: Jul 2007
Posts: 265
W
Member
I am with John on this one. polaris connectors are the way to go, hope it is a BIG gutter!


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
sudsy4:

The 8 barrel Polaris is <11" long, with cable entry from either side. So, you need a troff at least 12".

They make a 'stacker' model also, but...it's not UL Listed.

Check out the link below.

http://www.polarisconnectors.com/pdfs/NSi/IPLD_series.pdf


John