|
0 members (),
560
guests, and
20
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Apr 2002
Posts: 197
OP
Member
|
Can the low-volt wiring to a generator annunciator panel pass through the same junction box (without a partition) containing low-volt wiring corresponding to medical gas valves, gauges, and controls in a hospital?
|
|
|
|
Joined: Dec 2002
Posts: 337
Member
|
I do not know, but I would ask myself this as a quick test to say no. Is the system that I plan on mixing with a critical system. If it were I would not ask any further. My opinion here is not worth anything, but I noticed you were on rright now and that no one had responded.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
I have to agree with sabrown. I can't put a specific article on it. It's best to stay away from the critical system.
John
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
Is this a 517.30(C)(1) thing? What is the generator doing?
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Greg: IMHO, to provide an answer of allowed or not, a lot more details would have to be provided by the OP. He mentioned 'critical system', gas valves, control and no specific area for the 'j' box. I'm curious if he has any plans/specs. for the install.
John
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
I don't know if Ann. wires come into this but read . 700.9 (B) p. 1108 2008 handbook & (D)3 page 1112 2008 nec code handbook.
Yoopersup
|
|
|
|
Joined: Apr 2002
Posts: 197
OP
Member
|
Medical gases are oxygen, nitrogen oxide, and oxygen. They are piped to many rooms in a hospital. Gauges read their pressures and go into alarm when not within spec. I never mentioned "critical systems" but of coarse the most important purpose of the generator in a hospital is to provide critical and emergency power when called upon to do so. Generator annunciator wiring is not circuit wiring. Both the med-gas and generator wires I am describing are for status indicating only. The conductors feeding the gas valves I mentioned before are actually fed separately.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
On the face of it, I would say no. Make life easier for yourself and just run a seperate conduit. At least then there will be no question of your stuff mucking up anything that has been pre-installed. Even though we are talking about low-level signalling stuff here, its best to have some sort of segregation, even if for fault-finding purposes down the track. By that I mean, who hasn't opened up a but of wire troughing and found a tonne of wires all the same colour?
Also with new conduit, you have the opportunity to identify your work as being say "GEN-ANN" along the way.
Just my thoughts.
|
|
|
Posts: 61
Joined: August 2007
|
|
|
|
|