The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204127 - 11/14/11 07:37 PM mixing of systems?
triple Offline
Member

Registered: 04/01/02
Posts: 162
Loc: Wisconsin
Can the low-volt wiring to a generator annunciator panel pass through the same junction box (without a partition) containing low-volt wiring corresponding to medical gas valves, gauges, and controls in a hospital?

Top
#204136 - 11/15/11 05:48 PM Re: mixing of systems? [Re: triple]
sabrown Offline
Member

Registered: 12/12/02
Posts: 283
Loc: Ogden, Utah, USA
I do not know, but I would ask myself this as a quick test to say no. Is the system that I plan on mixing with a critical system. If it were I would not ask any further. My opinion here is not worth anything, but I noticed you were on rright now and that no one had responded.

Top
#204137 - 11/15/11 06:52 PM Re: mixing of systems? [Re: triple]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
I have to agree with sabrown. I can't put a specific article on it. It's best to stay away from the critical system.
_________________________
John

Top
#204139 - 11/15/11 08:16 PM Re: mixing of systems? [Re: triple]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
Is this a 517.30(C)(1) thing? What is the generator doing?
_________________________
Greg Fretwell

Top
#204140 - 11/15/11 09:42 PM Re: mixing of systems? [Re: triple]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Greg:
IMHO, to provide an answer of allowed or not, a lot more details would have to be provided by the OP. He mentioned 'critical system', gas valves, control and no specific area for the 'j' box. I'm curious if he has any plans/specs. for the install.
_________________________
John

Top
#204161 - 11/17/11 12:15 PM Re: mixing of systems? [Re: triple]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
I don't know if Ann. wires come into this but read .
700.9 (B) p. 1108 2008 handbook & (D)3 page 1112 2008 nec code handbook.

Yoopersup

Top
#204186 - 11/18/11 08:06 PM Re: mixing of systems? [Re: triple]
triple Offline
Member

Registered: 04/01/02
Posts: 162
Loc: Wisconsin
Medical gases are oxygen, nitrogen oxide, and oxygen. They are piped to many rooms in a hospital. Gauges read their pressures and go into alarm when not within spec. I never mentioned "critical systems" but of coarse the most important purpose of the generator in a hospital is to provide critical and emergency power when called upon to do so. Generator annunciator wiring is not circuit wiring. Both the med-gas and generator wires I am describing are for status indicating only. The conductors feeding the gas valves I mentioned before are actually fed separately.

Top
#204193 - 11/19/11 02:11 AM Re: mixing of systems? [Re: triple]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8344
Loc: SI,New Zealand
On the face of it,
I would say no.
Make life easier for yourself and just run a seperate conduit.
At least then there will be no question of your stuff mucking up anything that has been pre-installed.
Even though we are talking about low-level signalling stuff here, its best to have some sort of segregation, even if for fault-finding purposes down the track.
By that I mean, who hasn't opened up a but of wire troughing and found a tonne of wires all the same colour?

Also with new conduit, you have the opportunity to identify your work as being say "GEN-ANN" along the way.

Just my thoughts.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top