The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#204253 - 11/22/11 07:47 PM Re: Article 511 Required sealing [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Yoop:
A pic is worth 1000s of words. What you refered to as a 'box' is a troff, with feeders (or service), not what I thought was a 'device box'.

From the pic...yes, it is in concrete....but, NOT inside the wall; that may be why you bought a red sticker.

Personally, from what I see in the pic...I would not have any issue.

What Article did the AHJ write the violation on??
_________________________
John

Top
#204265 - 11/23/11 07:31 AM Re: Article 511 Required sealing [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
The walls are Acrylic Membrane as its only a temp. structure and there well never be True walls. Thus the concrete section. as in the photo.
Wrote it for going thur classified area without sealing . Did not list code section.It was not written on me but to contractor on site.

Top
#204308 - 11/28/11 07:55 AM Re: Article 511 Required sealing [Re: Yoopersup]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
I agree with John, that the service wires are encased in concrete so that they are "not in the building". We have to use that technique to get service conductors into the building along a wall into the service equipment. When the service equipment isn't real close to the point of entry.

Top
#204349 - 12/01/11 03:46 PM Re: Article 511 Required sealing [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
The Inspector said if you remove the Concrete it would be OK. According to him the Concrete brought the Floor level up to the top of the concrete??????
90.4 I guess.

Top
#204353 - 12/01/11 07:08 PM Re: Article 511 Required sealing [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
So, based on that 'logic' the vapors sorta balance themselves on the top of the concrete??? The vapor that was at the floor level where the concrete is magically 'jump'. (Where are the smiley faces)

I hate to say this, but if I received a red tag with that flimsy reasoning....it would time to go to the Board of Appeals. I know that doing so could end up putting me in a 'bad taste' with this AHJ, but this is crazy.
_________________________
John

Top