ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by tortuga - 03/18/24 08:39 PM
240V only in a home and NEC?
by tortuga - 03/18/24 04:29 PM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
Test Post
by sabrown - 03/06/24 05:29 PM
Solar PV Wiring Errors
by renosteinke - 03/02/24 09:12 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 94 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#204072 11/07/11 12:14 PM
Joined: Nov 2007
Posts: 764
K
KJay Offline OP
Member
I just recently bought a box of the Raco 4714 "Insider" inside-the-box connectors for the first time. I think these have been around for a while, but I can’t say that I’ve ever used them before. These are neat for old work, like fishing a wire into a box or panel that’s flush mounted in a finished wall. They have a pretty good range of wire combinations and I particularly like that they are almost perfectly flush with the inside of the box when installed, so they don’t take up any additional space when used with something like an octagonal box. Seems that Hubbell currently only makes them for 1/2" K.O’s., but it would be great if they could also offer them in 3/4" and 1" to handle 8/3 and 6/3 NM. I know Rack-a-tiers has made a similar type of 1/2" NM cable connector for years, but I don’t really like how far theirs protrude when installed from inside the box.

Raco Insider

Joined: Jul 2004
Posts: 9,919
Likes: 30
G
Member
Raco sent me a handful to evaluate. They do look like a good solution for some retro installations.


Greg Fretwell
Joined: Nov 2007
Posts: 764
K
KJay Offline OP
Member
One thing that caught my attention was where they say that these are the only NM cable connector listed for use in eccentric knockouts…. What?
I have to admit that is not something that ever even crossed my mind before when using any NM cable connector. I always thought that the eccentric/concentric KO concern was about grounding and bonding with metal raceways, especially for service equipment or for over 250V.

So this got me to thinking, which is never a good thing, about MC or AC and FMC type connectors used with eccentric KO’s.
Looking at MC connectors in the 2011 White book, it says they are considered suitable for grounding in circuits over and 250V, when installed in accordance with the NEC. So hopefully that means they are suitable for use with both concentric and eccentric KO’s as is, without the need for bonding bushings or grounding locknuts, even for circuits over 250V.


METAL-CLAD CABLE CONNECTORS,
TYPE MC (PJOX)
GENERAL

Grounding — Metal-clad cable connectors for use with metal-clad interlocking
armor ground cable, corrugated aluminum or copper tube, or
smooth aluminum tube, are considered suitable for grounding for use in
circuits over and under 250 V and where installed in accordance with
ANSI/NFPA 70, ‘‘National Electrical Code.’’

Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

I still have some of them from when I was in business. I think Raco is playing smart by getting them listed for eccentric knockouts, as KJay says, most of us probably don't even give eccentric KO's a thought when it comes to NM connectors.