The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#203624 - 10/13/11 12:54 PM Static Line as Grounding conductor
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
Can a Static Line be used to Ground HV (4160 0r 13.8 Impedience grounded systems between buildings on poles??
I think your either required to have a Neutral or Grounding conductor.
Yoopersup

Top
#203691 - 10/19/11 04:04 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
George Little Offline
Member

Registered: 01/18/04
Posts: 1445
Loc: Michigan USA
Ernie— I don't see anyone responding to your question and I think that possibly they don't understand the question or some of the terms you are using. I've been in the trade for 45+ years and I thought I understood quite a bit about code and I don't know what you are asking. Hope I'm not the only one. Maybe you could either elaborate or re-word the question or give us more details.

See Ya at the EAB meeting on the 3rd.
_________________________
George Little

Top
#203699 - 10/20/11 01:56 AM Re: Static Line as Grounding conductor [Re: Yoopersup]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
I was waiting for an explanation too. My guess is "static line" refers to the bare messenger and that is usually also the neutral but I could easily be wrong.

My experience looking at FPL is they use the grounded conductor on top for high voltage transmission lines and it is on the bottom for medium voltage distribution, below the 120/240.
_________________________
Greg Fretwell

Top
#203700 - 10/20/11 07:24 AM Re: Static Line as Grounding conductor [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
I sent Yoop a PM the day he posted this asking for some additional info. My thoughts went toward some type of 'mining' equipment.
_________________________
John

Top
#203712 - 10/20/11 12:13 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
Static Line : Definition
A Grounded wire at the Very top of the Pole intended to protect lower conductors from lighting.
Impedience Grounding is grounding thur a Neutral Ground Resister.(Limits fault current to ground) see 250.186.
My Question : Static line can it be used as a grounding conductor as 250.4 (A) 5 requires.
I Know it can't be used as a Neutral.But as a Ground??
Its refered as a Static line on the prints.
This apply to a 13.8 & a 4.16 over head & underground Customer owned Feeder.

Top
#203715 - 10/20/11 01:29 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Yoop:

Some quick research brought this up...

250.184 Solidly Grounded Neutral Systems.
Solidly grounded neutral systems shall be permitted to be either single point grounded or multigrounded neutral.
""For systems over 1000 volts, the Code permits solidly grounded neutral systems that are either single-point grounded or multigrounded systems. For the 2005 Code, 250.184 was reorganized, and new requirements for the installation of single-point grounded systems were added. Circuits supplied from a single-point grounded system are required to have an equipment grounding conductor run with the circuit conductors, and this conductor is not to be used as a conductor for continuous line-to-neutral load.""

Text within the double quotes ("") is commentary from 2008 NEC Handbook.
_________________________
John

Top
#203717 - 10/20/11 03:31 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
This is an Impedance grounded system not solidly grounded.
Yoopersup

Top
#203718 - 10/20/11 04:05 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
Tesla Offline
Member

Registered: 06/16/04
Posts: 768
Loc: Sacramento, CA
I wouldn't dream of tapping into any conductor that is designed to ATTRACT lightning.

Sure, it'd work okay most of the time...

Then, blammo, lightning races across your grounding grid at the speed of light.
_________________________
Tesla

Top
#203719 - 10/20/11 05:04 PM Re: Static Line as Grounding conductor [Re: Tesla]
ampherder Offline
New Member

Registered: 09/29/11
Posts: 3
Loc: VA
Speed of light?

Top
#203721 - 10/20/11 06:04 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
The only reason I question that logic is FPL puts the ungrounded conductor on the top of the pole in MV distribution. (and this is Florida where we have a lot of lightning)
_________________________
Greg Fretwell

Top
#203928 - 10/31/11 03:47 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
Explain myself a bit better,
4160 & 13.8 Y sysyems Impedance (NGR) grounded Systems.
Start off underground 3 phases & Ground from equipment.
Then hit a pole Line go up pole Ground wire ties to Static Line runs lenght of pole line.
Drops back down to Ductbank ties back into 3 phases & ground wire.
Static line Grounded to ground rod at each pole.
CAN a static line be used for this Purpose????
This is all Feeders Owners Equipment.
Yoopersup
I miss anything??

Top
#203934 - 10/31/11 07:01 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Yoop:

As I understand your question, IMHO, as long as the AWG of the 'static line' is compliant with the OCP, I see no reasoning why you can't use it. It is NOT a neutral.

Text from what I believe is the relevant Article (2011)
"250.186 Impedance Grounded Neutral Systems. Impedance
grounded neutral systems in which a grounding impedance,
usually a resistor, limits the ground-fault current
shall be permitted where all of the following conditions are
met:
(1) The conditions of maintenance and supervision ensure
that only qualified persons service the installation.
(2) Ground detectors are installed on the system.
(3) Line-to-neutral loads are not served.
Impedance grounded neutral systems shall comply with
the provisions of 250.186(A) through (D).
(A) Location. The grounding impedance shall be inserted
in the grounding electrode conductor between the grounding
electrode of the supply system and the neutral point of
the supply transformer or generator.
(B) Identified and Insulated. The neutral conductor of an
impedance grounded neutral system shall be identified, as
well as fully insulated with the same insulation as the phase
conductors.
(C) System Neutral Conductor Connection. The system
neutral conductor shall not be connected to ground, except
through the neutral grounding impedance.
(D) Equipment Grounding Conductors. Equipment
grounding conductors shall be permitted to be bare and
shall be electrically connected to the ground bus and
grounding electrode conductor.
_________________________
John

Top
#203941 - 11/01/11 04:48 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
Back to Question:
Can a Static Line Be used as A equipment Grounding conductor????
Remember on prints its noted as a STATIC Conductor.
Not a Equipment grounding conductor.
Might be OK I'd just like to see where thats Stated.
Yoopersup
(Thanks for all the imput)

Top
#203942 - 11/01/11 06:23 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Yoop:

I did a quick search in the '08 handbook (CD) and got zero hits on static line. You (us) may have to dig into the NESC for this one. As I said above, I see no reason you can't use it as of now.
_________________________
John

Top
#203958 - 11/02/11 04:44 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 737
Loc: Michigan
Theres different Definations for a Satic line & an Equipment Equipment grounding conductor.
Neither refers to the other.
The NEC is behind in the High Voltage Area.
Then throw in that its an Impeadence Grounding System.
That makes it even more interesting.
If you come up with anything conrete let me know John .
Yoopersup

Top
#203962 - 11/02/11 06:56 PM Re: Static Line as Grounding conductor [Re: Yoopersup]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Yoop:

Have you looked thru the 2011 NEC, or the NESC?

I have NESC at work, time permitting tommorrow.....

'11 is in my car, maybe reading materials tonite.
_________________________
John

Top