The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#203549 - 10/07/11 09:33 PM Article 410.10 D
sparkync Offline
Member

Registered: 10/17/02
Posts: 583
Loc: NC
I have a customer who wants to put a chandelier over the jecuzzi in the master bath. According to Article 410.10 D
of the 2011 code, it can't be within 3 ft. horizontally of the bathtub rim or 8ft. vertically, and it has to be marked for damp locations. What is your interpretation of putting the chandelier out 3ft. from the jecuzzi, and still mounted on an 8ft. ceiling? Does the 8ft. rule still apply if it's not over the jecuzzi? Thanks for your input. Also, they may have a problem finding a chandelier marked for damp locations. Thanks again.. Steve

Top
#203550 - 10/08/11 02:15 AM Re: Article 410.10 D [Re: sparkync]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
They are talking about a restrictive box 8' high and 3' wide above the rim and out from the tub.

If you are more than 3' out from the tub or more than 8' above the rim to any part of the fan or light, you are out of the box.
_________________________
Greg Fretwell

Top
#203552 - 10/08/11 11:17 AM Re: Article 410.10 D [Re: sparkync]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 649
Loc: Chicago Illinois USA
As I recall that 8' above the rim measurement is made to the lowest point of the light, not to the box that it's mounted to.

Be sure to check for any local Amendments.
Some of the suburbs around here require that it also be fed protected by a GFI circuit; and there's one that prohibits it being mounted above the tub no matter how high it is.
_________________________
Ghost307

Top
#204037 - 11/04/11 11:18 PM Re: Article 410.10 D [Re: sparkync]
mikethebull Offline
Member

Registered: 03/18/07
Posts: 79
Loc: Rhode Island
ghost 307 is right the 8 ft. measurement is from the finished fixture.

Top