The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#203194 - 09/14/11 06:10 AM Installation by landscape contractors!
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3298
Loc: Boston, Massachusetts USA
Here's a video clip showing the installation of some PVC by landscape contractors. This is electrical work and should be done by licensed electricians! Underground installation in a park
_________________________
Joe Tedesco, NEC Consultant

Top
#203204 - 09/14/11 12:22 PM Re: Installation by landscape contractors! [Re: Joe Tedesco]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
Is this low voltage for sprinklers or line voltage?
_________________________
Greg Fretwell

Top
#203206 - 09/14/11 12:56 PM Re: Installation by landscape contractors! [Re: Joe Tedesco]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Common trade practice regarding conduit has been that 'laborers' are allowed to install it. Duct banks for data/comm around here, are all 'laborer' installs. As far as I am aware, our POCO uses 'laborers' also. Keep in mind that these 'laborers' are union.

The cable/wire is 'sparkies' or CWA guys.

An old tale around here is 'once upon a time, the electricians were 'to busy' to want the UG pipe work'. Lately, the 'story' ahs changed, due to guys being 'not busy'; but it's too late.
_________________________
John

Top
#203208 - 09/14/11 01:17 PM Re: Installation by landscape contractors! [Re: Joe Tedesco]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
Landscape guys do all of the sprinkler work here. Generally, as long as it is the typical 24vac, the AHJ does not get too concerned. They just want to be sure the controller plugs into a compliant 120v GFCI receptacle (in use cover etc)
The sprinkler valve wires usually get run with the pipe.
_________________________
Greg Fretwell

Top
#203209 - 09/14/11 01:38 PM Re: Installation by landscape contractors! [Re: Joe Tedesco]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Greg:
Ditto on the lawn irrigation up here.

From the video, it sure don't look like it's an irrigation job!
_________________________
John

Top
#203264 - 09/17/11 10:20 AM Re: Installation by landscape contractors! [Re: Joe Tedesco]
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
The rules in 300.5 for a warning ribbon above the conduit applies to service conductors only, not encased by concrete.

So Joe must have known that this was going to be used for a service, and not for any other use, such as a feeder, communications,etc.


Top
#203265 - 09/17/11 10:36 AM Re: Installation by landscape contractors! [Re: Joe Tedesco]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
I suspect he "knows" what he could see through the fence.
_________________________
Greg Fretwell

Top
#203266 - 09/17/11 10:56 AM Re: Installation by landscape contractors! [Re: Joe Tedesco]
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3298
Loc: Boston, Massachusetts USA
I was unable to determine what type of system it was and will go back this week and check. It probably was not a service lateral. I called out the rule in my clip because I was more concerned with the lack of "qualified persons" who were not licensed here doing the work! wave I was not even sure as to the voltage, goes to show you, that when you are an old man that you have to be careful. dunno
_________________________
Joe Tedesco, NEC Consultant

Top
#203267 - 09/17/11 11:14 AM Re: Installation by landscape contractors! [Re: Joe Tedesco]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
FPL uses "contractors" (2 guys and a mini Kabota) to put in underground service laterals. The real electricians come in later to make the connections.
Your pictures look pretty normal to me.
Back in the happy days when things were busy most ECs also contracted out the digging. These days they do the work themselves, much to the dismay of guys who hate digging.
_________________________
Greg Fretwell

Top
#203275 - 09/18/11 08:58 AM Re: Installation by landscape contractors! [Re: Joe Tedesco]
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
SoCa Edison has "contractors" installing the ducts around here too. It doesn't matter if they're electricians or not. The same goes for transformer pads, hand holes, etc.

A SCE inspector will inspect the open trench, slurry when required, mandrel test the ducts, and give the approval for backfill.

The first time SCE has any "electricians" on the job is when they set transformers and pull the conductors into the ducts.

Top