The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#202677 - 08/21/11 12:59 PM Tankless Hotwater heater
dougwells Offline

Member

Registered: 05/03/03
Posts: 1126
Loc: kamloops BC Canada
I have an inquiry about installing a circuit for this Item.
Will this need a sub panel and am a bit rusty about the feeder size for the a sub panel.
Has anyone installed on of these thanks.
This will be a renovation


http://www.e-tankless.com/stiebel-eltron-tempra-29-tankless-water-heater.php

Top
#202678 - 08/21/11 08:54 PM Re: Tankless Hotwater heater [Re: dougwells]
Tesla Offline
Member

Registered: 06/16/04
Posts: 768
Loc: Sacramento, CA
"3 x 50 AMP breakers (depends on local codes)"

Each breaker at 240 VAC

"Minimum 3 x #8 AWG Copper (depends on local codes)"

So you'll need at least #8 -- but more likely #6 conductors.

(I'm assuming that you'll be dealing with a 60 degree panel board and or are using Romex. Otherwise, you'd be able to use #8.)

-----

I've never installed such a beast.

Instead I've installed insta-hots 30A @ 208 or 277...

You'll have to deal with line-of-sight disconnecting means -- which normally is addressed by a sub-panel rated 150 Amps @240VAC.

You can pipe and wire the feeder -- or use MC -- they make it big, BTW.

MC is available all the way up to 705 kCMIL. (!)
_________________________
Tesla

Top
#202679 - 08/21/11 09:54 PM Re: Tankless Hotwater heater [Re: dougwells]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I am a little suprised at the electrical layout. The manufacturer is suggesting three breakers to a single control panel. How do you effectively isolate the unit for service, normally there is a single point of isolation on the control panel such as a service switch on the front of it.

Also, from the drawing (page 13) it looks like the exposed L1/L2 terminals are right next to the inlet and outlets ports for the water piping. The drawings show wires running right past the mechanical piping within the control panel. Unusual to say the least that there seems to be no barrier between the sections.