The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#202037 - 07/11/11 07:23 PM AC90 protection
mersadrad Offline
Member

Registered: 03/11/11
Posts: 27
Loc: Montreal, Quebec, Canada
I want to ask in case i dont have antishort am I alowed to use electrical tape as a protection.
_________________________
“If you don't know where you are going, any road will get you there”.

Top
#202046 - 07/12/11 10:17 PM Re: AC90 protection [Re: mersadrad]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
CEC 12-610 (1) ".....bushings of insulating material or equivalent devices." But consider subrule (3) which requires the protection to be visible for inspection when cable is installed in connector or clamp. So as long as the electrical tape is installed with that in mind it should be okay. Anti-shorts are preferred because they are quicker, easy to see and more reliable.

Top
#202268 - 07/28/11 05:58 PM Re: AC90 protection [Re: mersadrad]
mikesh Offline
Member

Registered: 06/07/06
Posts: 567
Loc: Victoria, BC, Canada
Tape vs anti short? I would not permit electrical tape to replace an anti short. Tape is too susceptible to cutting by the armour of the BX and it cannot be placed in between the armour and the wire either. In fact the insulation of the wire is already more resistant to cutting than tape itself. So what use is tape in this application?

Top
#202276 - 07/29/11 11:13 AM Re: AC90 protection [Re: mersadrad]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Mike,

My intent with referencing section 12 was just to say there is no specific reference to "anti-shorts" but it does reference insulating material or equivalent, leaving room for interpretation.

I have torn anti shorts while installing on bx, and I have always been able to wind back the armour enough that I could get several layers of tape on if needed. But I know that you are with inspections, so your post carries some weight.

Top
#202279 - 07/29/11 12:52 PM Re: AC90 protection [Re: mersadrad]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Just an FYI from 'south of the border" (2008 NEC)

320.40 Boxes and Fittings.
At all points where the armor of AC cable terminates, a fitting shall be provided to protect wires from abrasion, unless the design of the outlet boxes or fittings is such as to afford equivalent protection, and, in addition, an insulating bushing or its equivalent protection shall be provided between the conductors and the armor. The connector or clamp by which the Type AC cable is fastened to boxes or cabinets shall be of such design that the insulating bushing or its equivalent will be visible for inspection. Where change is made from Type AC cable to other cable or raceway wiring methods, a box, fitting, or conduit body shall be installed at junction points as required in 300.15.

Looks like we are basically on the same page on this.
_________________________
John

Top
#202292 - 07/29/11 11:04 PM Re: AC90 protection [Re: mersadrad]
twh Offline
Member

Registered: 03/11/04
Posts: 607
Loc: Regina, Sask.
Use red tape.

Top
#202293 - 07/30/11 12:15 AM Re: AC90 protection [Re: mersadrad]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1126
Loc: kamloops BC Canada
Someone must sell the larger antishorts, but none of the suppliers here do. They just say everyone uses tape.

Top
#202314 - 07/30/11 07:19 PM Re: AC90 protection [Re: mersadrad]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Doug:
It's been awhile, but there used to be a bag of red heads attached to every roll of BX.
_________________________
John

Top
#202315 - 07/30/11 07:31 PM Re: AC90 protection [Re: mersadrad]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1126
Loc: kamloops BC Canada
Yes for BX, need red heads for cable sizes #6 AWG and up smile. This cable has just a thin wrap of paper between the conductors and the sheathing btw it is an aluminum conductor cable assembly

Top