The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (twh), 93 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#201882 - 06/29/11 10:22 AM Re: sealing of cables in U/G sump pump installations [Re: bigpapa]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
this thread also raises an interesting point - reference is to parking garage sump which would have a hazardous location category assigned to it. But the motors are not rated for hazardous category and the wiring method is cabtire which is also not rated for hazardous location to my knowledge.

Top
#202041 - 07/12/11 12:03 AM Re: sealing of cables in U/G sump pump installations [Re: bigpapa]
bigpapa Offline
Member

Registered: 03/18/06
Posts: 62
Loc: canada
Found this on the City of Surreys web site

www.surrey.ca/files/ParkadeSumpDetails1.pdf

Seems to mirror this thread regarding the hazardous area.
One point to remember is the pump controller must have an intrisic barrier. I would have guessed that the cabtire cable connectors would serve this purpose but perhaps not. The pump controller would always be above the classified area.

Top
#202044 - 07/12/11 04:13 AM Re: sealing of cables in U/G sump pump installations [Re: bigpapa]
twh Online   content
Member

Registered: 03/11/04
Posts: 607
Loc: Regina, Sask.
I don't think that I've seen a controller with an intrinsic barrier.
http://en.wikipedia.org/wiki/Intrinsic_safety