by ale348 - 03/29/24 01:09 AM
by NORCAL - 03/19/24 05:11 PM
#201431 05/31/11 10:56 PM
Cinner Offline OP
On a 3 phase panel - if 2 circuits share a neutral - do you have to use a 2 pole breaker so that if one trips they both trip?
twh Offline
14-010. It depends on whether the circuit feeds lights or plugs.
It isn't a trip issue, though. We can still use fuses as long as we include a disconnect that meets the requirements of 14-010(b).
twh #201442 06/01/11 01:57 AM
Cinner Offline OP
It is for receptacles. Can you use 15 amp single pole breakers if the neutrals are being shared to more than one circuit?
the trade practice for three phase 4 wire circuits feeding 120/347 volts loads is single pole breakers. I could see good justification for a three pole breaker to ensure a circuit is completely disconnected included any current on a shared neutral but I dont think any code rule requires it. If the receptacle/load is using more than one phase then you need to use 2 or 3 pole breaker.
jay8 #201447 06/01/11 04:30 PM
and before a bunch of posts come about the implications of common breaker handle for single phase loads, I can see some change in installation practice that will reflect the issue of current on shared neutral - such separate neutrals etc
