The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

Unique and Innovative Tools for Electricians, Electrical Contractors, Maintenance and Telecom Professionals
Tools for Electricians

   
Recent Posts
Unique Exhaust Fan Control Request
by ghost307
Yesterday at 06:22 AM
Incorrectly Wired Switch
by thomaslong
06/28/16 12:30 AM
How is this not a ground fault?
by gfretwell
06/27/16 09:06 PM
Sub-panel off the "back of the meter"
by BigB
06/27/16 09:03 PM
Speaking of Plugmold ...
by ghost307
06/26/16 11:55 PM
New in the Gallery:
GE 90 MW Generator
Shout Box

Top Posters (30 Days)
gfretwell 38
HotLine1 27
renosteinke 18
ghost307 16
twh 16
Who's Online
1 registered (HotLine1), 167 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#200885 - 04/25/11 12:36 PM Difference in AC and DC disconnects
bwise121 Offline
Member

Registered: 09/11/03
Posts: 113
Loc: Sacramento, CA USA
I just put in my first DC disconnect and for the life of me I can't see what the physical difference is. Besides the fuses is there a difference? Is there such a thing as a non-fused disconnect?

Thanks,
Byron

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#200886 - 04/25/11 12:56 PM Re: Difference in AC and DC disconnects [Re: bwise121]
Vindiceptor Offline
Member

Registered: 03/28/11
Posts: 98
Loc: San Diego
Is this a PV DC disconnect?

Some manufacturer's have different arc chutes and most will require the use of multiple poles being used to facilitate the breaking of the DC arc.

Square D and Siemens both have wiring diagrams, have not used a Cutler-Hammer Disconnect yet.

Yes, you can get them as non-fused.


Edited by Vindiceptor (04/25/11 12:58 PM)

Top
#200887 - 04/25/11 01:47 PM Re: Difference in AC and DC disconnects [Re: bwise121]
bwise121 Offline
Member

Registered: 09/11/03
Posts: 113
Loc: Sacramento, CA USA
Yes, it is a 30 amp disconnect for a PV system.

Top
#200888 - 04/25/11 01:58 PM Re: Difference in AC and DC disconnects [Re: bwise121]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 8970
Loc: Estero,Fl,usa
You can usually put a big diode across a DC contact to put out the fire.
_________________________
Greg Fretwell

Top
#200889 - 04/25/11 05:50 PM Re: Difference in AC and DC disconnects [Re: bwise121]
Vindiceptor Offline
Member

Registered: 03/28/11
Posts: 98
Loc: San Diego
Originally Posted By: bwise121
Yes, it is a 30 amp disconnect for a PV system.


2 or 3 pole and how did you route the circuit through the disconnect?

What's the Isc for the circuit? That would determine whether you can run the circuit through a single pole, 2 or three (when 2 is required and you have a fuse, some manufacturer's want the fuse in the center pole 'B phase').

You can NOT route a circuit through a single pole and maintain the UL listing of the switch, Square D used to imply that you could, but they have since reworded their documentation.

I'm only mentioning this because I've seen a LOT of botched/non-code compliant designs and installs using 30, 60, 100 and even 200 amp 600 VDC disconnects with 3 circuits going through them.

We have been using combiner boxes with integral DC disconnects since mid 2009 because of the confusion with AHJ's, unfortunately, most don't even know what they're looking at when they're inspecting them, but they are definitely getting better and more informed since the PV market blew wide open.

Top
#200894 - 04/26/11 10:38 AM Re: Difference in AC and DC disconnects [Re: gfretwell]
LarryC Offline
Member

Registered: 07/05/04
Posts: 771
Loc: Winchester, NH, US
You can usually put a big diode across a DC contact to put out the fire.

How will that help if the load is not inductive? The diode shorts out the inductive kick from a collapsing magnetic field because the induced voltage is the opposite polarity. A diode or even a RC network across contacts won't do much if the DC load is not inductive.

Top
#200895 - 04/26/11 10:57 AM Re: Difference in AC and DC disconnects [Re: bwise121]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 8970
Loc: Estero,Fl,usa
Non inductive loads break cleaner.
_________________________
Greg Fretwell

Top
#200897 - 04/26/11 02:37 PM Re: Difference in AC and DC disconnects [Re: bwise121]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
The DC from PV arrays is NOT an infinite bus.

It breaks MUCH cleaner for that reason.

There is only so much energy flowing into the PV cells.

So even shorted PV DC does not produce the astounding arcs expected.

Not that I'd recommend trying it.