#200440 04/01/11 05:06 PM
Joined: May 2003
Posts: 1,158
Member
I am looking for a safe way to deal with this item rerouting new loomex may not be an option at this time.
I was thinking load center with afci breakers.

[Linked Image from electrical-photos.com]


[Linked Image from electrical-photos.com]


[Linked Image from electrical-photos.com]

dougwells #200442 04/01/11 05:48 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I wouldn't use afci anywhere not required by code. They can have tripping problems.

gfi dead-fronts are less expensive than gfi breakers, but must sit outside the panel. gfi breakers look nicer.

It looks like you have 3 wire circuits, so you will need some 2 pole gfi breakers.

What is the new procedure for putting K&T into a knockout?

You don't have many circuits, so when you install 15 amp breakers, you might have a problem.

dougwells #200443 04/01/11 05:52 PM
Joined: May 2003
Posts: 1,158
Member
I was thinking loom over the wire and a 2 screw connector.
This must of been the old service at one time. There is a 100 amp panel in the basement now.
I definitely have to get him some fuse restrictors while working on this smile

dougwells #200444 04/01/11 05:53 PM
Joined: May 2003
Posts: 1,158
Member
Looks like I should megger everything to as there is 25 and 30 amp fuses installed atm.

And I dont think i have any neutrals too attach to a new load center for each circuit either

Last edited by dougwells; 04/01/11 05:55 PM.
dougwells #200445 04/01/11 06:01 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
No neutral = no gfi

dougwells #200446 04/01/11 06:03 PM
Joined: May 2003
Posts: 1,158
Member
Gee i think i found the the fuse panel that is in my avatar laugh

dougwells #200447 04/01/11 06:04 PM
Joined: May 2003
Posts: 1,158
Member
And ohh this is all mounted to the back side of a wall the "cover" is a piece of plywood . that white is some sort of abestos paper too

dougwells #200448 04/01/11 06:12 PM
Joined: May 2003
Posts: 1,158
Member
Ohh that 3 wire loomex is 10/3 and is feeding that mess.

dougwells #200450 04/01/11 06:32 PM
Joined: Jul 2004
Posts: 787
L
Member
Doug,

How about using the existing location as a splice box and run new wiring down to a centralized breaker panel?

dougwells #200451 04/01/11 06:38 PM
Joined: May 2003
Posts: 1,158
Member
I am wondering what year this stuff is from too.