#200327 03/28/11 09:48 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
[Linked Image]

Found this responding to a tenant complaint in building.

Fire Prevention followed me, they wrote nine (9) violations.

Interesting that a building that has done no electrical work...has yellow #12 NM


Last edited by HotLine1; 03/28/11 09:50 PM.

John
Joined: May 2003
Posts: 1,158
Member
I like it now that romex has a date of manufacture on it now also smile

Joined: Sep 2006
Posts: 155
C
Member
handymen don't actually do any "work"

Joined: Oct 2000
Posts: 5,392
S
Member
looks mighty familiar HotOne

but how do we know that the new RX was simply a service call to replace a bad wire by a bona fide sparky there?

~S~


Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
~s~:
Based on what I saw...the last 'bonafide sparky' there was the crew that wired the structure way back when!



John
Joined: Oct 2000
Posts: 5,392
S
Member
As is often the case Hotone

that said, other than working clearance, and a missing panel cover, can you tell us what violations were found?

~S~

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
~s~:
Synopsis of issues:
Missing/broken smoke & heat detectors.
Defective fire extinguisher.
The obvious panel clearance & open wiring
Missing covers on various j-boxes
Housekeeping issues; trash, waste debris
Inproper Flamable storage.
Blocked egress
Damaged sheetrock (wall/ceiling)



John
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Doug:
Just an FYI, I couldn't get close enough to the open panel to look for the date stamp. Yes, that's handy to have a 'date'.



John
Joined: Oct 2000
Posts: 5,392
S
Member
point taken

i sign & date all my installs

i also collect old code books, due to the term existing being predicated on a compliant install at the time

~S~

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
~s~:
I also have a collection of NECs, they sure come in handy on some 'old' jobs.



John