The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
05/23/12 06:34 PM
450.3(C)
by Tesla
05/23/12 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
05/23/12 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (Merlin), 96 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#192976 - 03/12/10 08:17 PM Re: Max distance of main panel from meter [Re: jdevlin]
twh Online   content
Member

Registered: 03/11/04
Posts: 607
Loc: Regina, Sask.
Quote:
It's 2 " of concrete not conduit
The likelihood of a typo increases by the square of the number of readers.

I understand the reason for the rule. It's the interpretations that are interesting. The phrase "as close as practicable" has distances and wiring methods attached. It's almost like we still have amendments.

Top
#199991 - 03/16/11 04:44 PM Re: Max distance of main panel from meter [Re: twh]
mersadrad Offline
Member

Registered: 03/11/11
Posts: 27
Loc: Montreal, Quebec, Canada
I would say that rule is made considering voltage drop. So "as close as posible" does not seem defined completly. Voltaage drop can't be more that 5%.
From service to main panel 2%.
From main panel to branch 3%.


Now I am still an apprentice so I might be wrong, that is why I like to ask questions. Forgive me if I am anoying.
_________________________
“If you don't know where you are going, any road will get you there”.

Top
#199995 - 03/16/11 06:06 PM Re: Max distance of main panel from meter [Re: twh]
pooL8 Offline
Member

Registered: 02/18/11
Posts: 51
Loc: Skeena Watershed
B.C. Directives say that any distance greater than 1.5m is considered unacceptable without prior consultation with Authority.
"To limit the risk of fire, because service conductors lack effective overcurrent protection."

Ummmmmmmm....

I'm wondering why that should be up to us to 'solve'. Afterall aren't conductors supposed to have effective overcurrent protection?

Put overcurrent protection in the meters is an idea. Then we can run them wires as far as practicable smile
Thanks Hydro! (I'll take one of those electric crimpers too)


Top
#199996 - 03/16/11 06:25 PM Re: Max distance of main panel from meter [Re: mersadrad]
mikesh Offline
Member

Registered: 06/07/06
Posts: 567
Loc: Victoria, BC, Canada
Originally Posted By: mersadrad
I would say that rule is made considering voltage drop. So "as close as posible" does not seem defined completly. Voltaage drop can't be more that 5%.
From service to main panel 2%.
From main panel to branch 3%.


Now I am still an apprentice so I might be wrong, that is why I like to ask questions. Forgive me if I am anoying.


The issue is unrelated to VD in this case. The conductors ahead of the main switch are considered to have no overcurrent protection. You probably have seen fuses on the pole top transformer that supplies the 6 to 10 houses you are all connected to. If one of the ungrounded (hot) wire faults to ground in a service raceway the utility transformer might see that bug bump in current as a load rather than a fault. I have certainly seen a few service panels and raceways burned completely away before the fuse on the transformer or a connection in the meter or triplex opens under the heavy current flow. If this service pipe was inside your walls it might set the house on fire before the fuse on the transformer blows. It is very common for utility transformers loaded to %200 of their rating when connected to residential services. In the case of the panels I have seen burned away I got to the house after the fire trucks.
By encasing the raceway in concrete it is hoped that the concrete will enclose the melting raceway and protect the combustible wall it is inside. Eventually the fuse will open or the raceway will burn away enough to stop conducting fault current.
Then there is the problem of theft from the utility. We have seen more than a few raceways cut open ahead of the meter to tap the utility wires. Pot growers seem to love to do this.

Top
#200000 - 03/16/11 07:33 PM Re: Max distance of main panel from meter [Re: mersadrad]
pooL8 Offline
Member

Registered: 02/18/11
Posts: 51
Loc: Skeena Watershed
Quote:
Forgive me if I am anoying
Okay... but I won't forgive you for saying THAT!

Dude. Some of us don't look down on 'apprentices' (people). Talk to us, not the ones that do.

Top
#200012 - 03/17/11 10:20 AM Re: Max distance of main panel from meter [Re: twh]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
If you have a situation where "as close as practicable" is not a good location for your panel, you could consider a fusible disconnect after the meter, then place your loadcenter where ever you need at whatever distance.

This is particularly suitable when the meter is mounted on a garage, so the disconnect can go inside the garage, or where there is room for a fusible disconnect inside the house but not a combination panel.

.

Top
#200058 - 03/18/11 06:32 PM Re: Max distance of main panel from meter [Re: pooL8]
mersadrad Offline
Member

Registered: 03/11/11
Posts: 27
Loc: Montreal, Quebec, Canada
I did service entrance 400A, 200A, and 100A. I do remember
connecting meter box. It is logic to fuse meter, but I never saw one (not plugged in).
So we need a disconect switch to be as close as posible.
_________________________
“If you don't know where you are going, any road will get you there”.

Top
#200065 - 03/18/11 11:23 PM Re: Max distance of main panel from meter [Re: mersadrad]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
I will quote both USA and France side with the max distance from meter to main panel the USA side it will varies a bit depending on which states they use that codes but most of them say short as possible so tyically less than 2 meters from the main meter but few do can go much as 4 or 5 the most.

In France we are limited to 3.5 max distance but most case they are useally on outdoor main disconnect switch.

Merci.
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)