triple Offline OP
Does a 1/2" copper condensate line mounted to the floor 3'3" back from the front of a 277/480V VFD violate condition 2 in table 110.26(A)(1)? This pipe (grounded part) is something that could get stepped on but not backed-into like a steel railing or concrete wall so why should it be seen any different than the concrete an electrician would be standing on? If it is a violation then apparently a ridge or step in the concrete floor (even one only a fraction of an inch high) at 3'3" back would also be against the NEC.
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
triple #198855 02/06/11 12:44 AM
SJT Offline
Triple,
The 3'3" is close to the 3'6" needed to satisfy the code. If the AHJ is saying it is in violation, could the condensate pipe be moved back, to keep peace?
SJT
triple #198890 02/07/11 10:38 AM
You could have them encase the cooper line in concrete but that might be a little too severe.