Where can I find the code requiring the removal of abandoned cables and conductors unless they are labled "spare" or "for future use"?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
There are rules in cellular raceway system, low voltage, alarm and data center articles but I don't know of anything specific in article 300 wiring.
Greg I don't know if this is relevant or not but 590.3(D) might apply depending on what the OP is talking about. And if it's one of the cables in Chapter 7 or 8 they need to be removed or tagged per XXX.25
George Little
triple Offline OP
Thank you Mr Little. That was the info I was looking for. Using your help and the additional information available in the Handbook, I found a total of ten articles related to this subject.