#198610 01/29/11 02:11 PM
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
Where can I find the code requiring the removal of abandoned cables and conductors unless they are labled "spare" or "for future use"?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
There are rules in cellular raceway system, low voltage, alarm and data center articles but I don't know of anything specific in article 300 wiring.


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Greg I don't know if this is relevant or not but 590.3(D) might apply depending on what the OP is talking about. And if it's one of the cables in Chapter 7 or 8 they need to be removed or tagged per XXX.25

Last edited by George Little; 01/29/11 06:10 PM.

George Little
Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
Thank you Mr Little. That was the info I was looking for. Using your help and the additional information available in the Handbook, I found a total of ten articles related to this subject.