Joined: Apr 2002
Posts: 197
T
triple Offline OP
Member
The lightning protection wire is run inside pvc through the building I am working on. However, a 50' stretch is run outside the pvc and simply strapped-up to the steel decking through the ceiling of one room. Surely this cannot be allowed? In the event of a lightning strike, couldn't the arcing and sparking created between the wire and the deck result in a fire?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2005
Posts: 91
G
Member
I can't think of an NEC violation, but it might run against the... NFPA 780? Whatever the lightning one is.


-George
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Lightning protection here (NJ) are installed by "Certified Installers" to the best of my knowledge. As an EC, the sites that I worked on (Country Clubs) had a lightning contractor.

What you described does not sound 'right', but that's just a off the cuff comment. All the conductors that I have noticed were routed on the exteriors of the structures.



John
Joined: Dec 2002
Posts: 337
S
Member
Just some items to be aware of besides the certified installer.

There is no typical requirement stating that the "down conductors" not allowed being run through the interior of a building. That being said, it does create alot more bonding issues that must be taken care of (flashovers).

There is no normal installation "shall" requirement that the conductors be in conduit.

But simply strapping a down conductor to steel decking does not meet bonding requirements assuming strapping means something to just hold the condutors in place (every 36" maximum). These are typically bonded via bonding plates or cadwelded. Whatever is used it is listed for lightning protection and has very specific requirements.

There are however requirements for regular yearly inspection of the system.

I am sorry that I can't put more information into this reply, but that would involve teaching a course on lightning protection.