ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 260 guests, and 32 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#198101 01/12/11 08:24 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
I have a client who has 3 UPS system with a total 10KVA capacity. They currently have a 30Amp feeder with a Subpanel in the communication room.
They have asked me to install a 60Amp feeder for additional UPS units.

here are the question/s that i have.
>I assume i need to have a disconnect within site of the UPS units? Right?
>I will size the feeders to 125%?
>Existing, the UPS feeds the Existing sub panel by a SOO cord, is that O.K.

Thank you for your input


Be kind to your neighbor, he knows where you live

Niko #198116 01/12/11 11:44 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Niko:

Yes to the disconnect.
125% is OK
Possibly OK, but more info is needed. Is the connection from the UPS via a cord cap? Is there frequent 'swapping' of the UPS? IF yes, then the cord could be acceptable.



John
HotLine1 #198117 01/13/11 12:57 AM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
There is no frequent swapping of UPS. Currently the UPS is cord & cap connected to the feeder receptacle sized 6AWG then the UPS feeds the subpanel sized 6AWG cord.





Be kind to your neighbor, he knows where you live


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5