#197580 - 12/07/10 10:10 PM
Re: TIA proposal Spa bonding
[Re: frenchelectrican]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
The real issue is the guy who drops a packaged spa on an existing concrete patio slab (no supplemental decking). The AHJs were requiring that they install a raised deck, nonconductive material, around the spa, out 3'. This was typically Trex or another plastic. This was to avoid tearing up the slab and putting in bonding. The spa stores have them as an accessory but I am guess the spa people thought, in tough times, it was hindering sales.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#197585 - 12/07/10 10:59 PM
Re: TIA proposal Spa bonding
[Re: gfretwell]
|
Member
Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
|
That is instering and I think it should come standard package when they land it on slab but on decking it should not be a issue but the other hand is the deck stucture itself that should be well built to withstand the weight of spa when it get filled with water in there.
Merci. Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
Top
|
|
|
|
#197588 - 12/08/10 01:12 AM
Re: TIA proposal Spa bonding
[Re: frenchelectrican]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
The deck kits do no go under the tub, they just ring it about 8" high and extend 3 or 4 feet out from the tub. That usually relieves them from the "paved surface" problem.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#197633 - 12/11/10 07:40 AM
Re: TIA proposal Spa bonding
[Re: gfretwell]
|
Member
Registered: 06/27/04
Posts: 464
Loc: massachusetts
|
The 2005 NEC requires the perimeter bond under "paved surfaces"...2005 680.26(C)(3) requires #8 grid in a 12x12inch network
The 2008 NEC requires the perimeter bond under "unpaved surfaces" as well as "paved surfaces"... 2008 680.26(B)(2)(b) requires a #8 single conductor as an alternate means...
For 2011, the code has gone back to the 2005 method with the requirement of the grid style perimeter bond...2011 680.26(B)(1)(b)(3)
Does anyone have the 2011 ROP with regard to the change back to the grid pattern?
|
|
Top
|
|
|
|
#197664 - 12/13/10 12:12 PM
Re: TIA proposal Spa bonding
[Re: renosteinke]
|
Member
Registered: 06/27/04
Posts: 464
Loc: massachusetts
|
I've looked at the ROP on the internet and I see nother regarding a 12x12inch network style grid for the perimeter bond for 2011. I made my statement from the article in the November issue of EC+M of code changes for the 2011 NEC.
I have not bought the 2011 NEC as I am waiting for the Massachusetts version.
Can anyone verify the 12x12inch grid for the perimeter in the 2011 NEC?
Thanks, shortcircuit
|
|
Top
|
|
|
|
#197668 - 12/13/10 02:27 PM
Re: TIA proposal Spa bonding
[Re: shortcircuit]
|
Member
Registered: 11/27/07
Posts: 729
Loc: MA, USA
|
The #8 solid copper conductor is still acceptable in the 2011 NEC for Perimeter Surfaces, 680.26[B],2,[b] Alternate Means.
|
|
Top
|
|
|
|
#197700 - 12/15/10 08:38 AM
Re: TIA proposal Spa bonding
[Re: KJay]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
Reno,
As I have been saying for awhile that the only pool I have ever seen problems with, are the pre-formed plastic/fiberglass pools. Only they seem to have stray voltage problems. Never seen stray voltage with concrete or steel pools.
|
|
Top
|
|
|
|
#197708 - 12/15/10 12:32 PM
Re: TIA proposal Spa bonding
[Re: harold endean]
|
Member
Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
|
That is one unspecified advantage of the "paved surface" bonding. You are creating a Ufer ground electrode at the pool and that will mitigate most stray voltage problems by minimizing ground shift. I often wonder if these stray voltage problems at a plastic pool could have been fixed with a couple ground rods but when you bury that #8 solid you have just made a ground ring.
A concrete pool will always be your best ground electrode, like it or not. By the time you do all the required bonding on a typical "caged" pool, you have included your pool in the ground electrode system anyway.
_________________________
Greg Fretwell
|
|