#196895 - 10/31/10 12:48 PM
Fire rated troffers/ceilings
|
Member
Registered: 01/01/01
Posts: 1063
Loc: Shinnston, WV USA
|
When installing a 2x4 troffer in a fire rated dropped ceiling, is anything required other than an FR rating on the fixture? I'm specifically interest in special covers that go over the fixture, such as the ones made by TENMAT.
I rarely get into work that requires fire ratings. I don't recall ever seeing anything special being done for a lay in troffer in the fire rated ceilings I've looked in.
Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
|
|
Top
|
|
|
|
#196926 - 11/01/10 07:54 PM
Re: Fire rated troffers/ceilings
[Re: renosteinke]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Tom: IF you have a rated ceiling assembly, then you must provide 'equal' rating with the devices you install.
First, check with the local AHJ & determine IF the drop ceiling is in fact a rated assembly. The mfg install instructions will be a big help in this also.
IF you have to maintain the rating, the Tenmat covers are the easiest approved for maintaining the rating.
Some 'old school' metgods were placing a 'tent' of 5/8" fire code sheetrock over the top & sides of a troffer. Another was laying 'rotten cotton' insulation over the fixture. Some AHJs accepted the described ways, others did not. The Tenmat is UL labeled/listed for troffers and rated ceilings. There may be other brands, but that is the only one I am aware of.
_________________________
John
|
|
Top
|
|
|
|
#196944 - 11/02/10 08:32 AM
Re: Fire rated troffers/ceilings
[Re: renosteinke]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Reno: I dd not stress this but...
" The mfg install instructions will be a big help in this also."
We all should know that a rated wall or ceiling assembly is installed to contain a fire (for a period of time) from penetrating the rated assembly. The integrity of the assembly must be maintained when any penetrations are made. (Lighting, HVAC diffusers, receptacle locations, etc) There are listed/labeled (UL Tested) items to insure the rating of the assembly.
The item the OP and I mentioned is UL for fixtures within a rated ceiling.
All that said, yes, there are 'rules' (specs) within the UL rating book, which limit/guide the number and spacing requirements of all penetrations in all rated assemblies.
Following the mfg instructions for the ceiling assembly and the mfg instructions for all items used to maintain the rating of the ceiling is paramont.
_________________________
John
|
|
Top
|
|
|
|
#196985 - 11/03/10 06:55 PM
Re: Fire rated troffers/ceilings
[Re: HotLine1]
|
Member
Registered: 06/16/04
Posts: 768
Loc: Sacramento, CA
|
The single touchiest drop ceiling I ever had the pleasure of messing with was for a Toys R Us build-out.
The Fire Marshall had his hair on fire when the retailer's all plastic and cardboard inventory, all the time, for children/fire bugs came to his attention.
So the lid was changed to fire proof and sprinklers aplenty. Further, even the gaps in the lid needed listed fire-stop.
The fixtures were mandated to be LOWER than the fire lid. Hence they could be ordinary 277v low-bays.
Correcting all of the circuit faults -- whew -- NOT fun.
Because of the Fire Marshal, EMT was preferred over MC at every turn. Getting his okay was solely based upon the level of craft and his opinion.
---------
Why was he so picky? Just the prior month a Toys R Us burned down on the East Coast in record time. Then the word went out to all of the other Fire Marshalls: these toy stores are 'Coconut Groves' waiting to happen!
_________________________
Tesla
|
|
Top
|
|
|
|
#196989 - 11/03/10 08:46 PM
Re: Fire rated troffers/ceilings
[Re: Tesla]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Interesting scenario Tesla. Was the store sprinklered prior to the fit-out? Sounds 'odd' that a retail space suitable for that tenant would not be sprinklered from the get-go.
_________________________
John
|
|
Top
|
|
|
|
#197006 - 11/04/10 06:18 PM
Re: Fire rated troffers/ceilings
[Re: HotLine1]
|
Member
Registered: 01/01/01
Posts: 1063
Loc: Shinnston, WV USA
|
Thanks for all the replies. The fixture manufacturer send me information on their fixtures, including links to UL Fire Resistive Assemblies.
In this particular case, I am the AHJ. The 1 hour fire rating is not mandated by code, but is a customer request & applies to one room only.
_________________________
Few things are harder to put up with than the annoyance of a good example.
|
|
Top
|
|
|
|
#197029 - 11/05/10 06:40 PM
Re: Fire rated troffers/ceilings
[Re: Tom]
|
Member
Registered: 06/16/04
Posts: 768
Loc: Sacramento, CA
|
It was sprinklered.
The east coast store... I don't know.
I do know that the FM triggered a fist full of extras for GC and EC....
Our management loved them.