ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
Joined: Aug 2010
Posts: 9
L
New Member
I've been reading everything I can find about wiring portable generators for backup power for houses. One thing I don't understand concerns the neutral. A common wiring method is to isolate the neutral and ground at the generator frame and solidly bond the generator neutral to the service neutral in the transfer switch, which is considered to effectively ground the generator (because the service ground is grounded at the transformer). This seems wrong to me. What if the meter is fed from an overhead service that is torn down during a storm? The service neutral (ground) is no longer grounded, nor is it grounded at the generator. This would seem to be an unsafe situation. Plus, since the return current from a 120V circuit would have 2 paths, mightn't it be possible to have some backfeed on the service ground, possibly endangering the lineman? If someone can answer this I have a couple of other questions.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The generator is grounded in your scenario by the grounding electrode conductor, not the neutral going back to the transformer. The power company also grounds the transformer to protect their people.


Greg Fretwell
Joined: Jul 2004
Posts: 787
L
Member
Remember you, the structure, already have a local ground at the service entrance.

Joined: Aug 2010
Posts: 9
L
New Member
It's my understanding that the GEC is only used to handle over voltage problems. The grounded wire is what's used to clear faults, that's why the GEC, the grounding and grounded wires are all bonded together at the service disconnect. If a grounding wire was only connected to a made electrode and a fault occured, there may not be enough current flow to trip a breaker. So in the scenerio above, with the generator neutral isolated from the ground and no service grounded wire, a fault to the circuit grounding wire would have one path back to the generator chassis (becoming a shock hazard) and a 2nd path from the transfer switch cabinet to the service panel and the GEC. Since the neutral is bonded to ground here and bonded to the generator neutral in the transfer cabinet, the fault will travel back to the generator neutral. I assume this would cause enough current flow to trip the overload on the generator. I suppose that would work, but it just doesn't 'feel' right. Makes more sense to completely isolate the 2 different power sources. But I guess that's why I'm not an electrical engineer.

Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
First, be clear on one thing: no one truly 'understands' electricity. ALL of our models have flaws, and 'unusual' situations usually underscore the weakensses of our models.

I am a strong supporter of transfer-switched neutrals specifically because of questions like these. I'd rather avoid the uncertainty.

Here's grounding in a nutshell: Electricity only wants to "go home." It does not want to go anywhere else.

For power from the power company, this means it wants to go back to the transformer that made it.

For generator-made power, this means it wants to get back to the generator.

For lightning, this means back to the planet surface.

The 'neutral' is nothing but a path 'home.'

Care to guess where the ground rod fits into all of this?

Joined: Mar 2005
Posts: 1,803
Member
It puts me at the same potential as the generator chassis?


Wood work but can't!
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Alan, you know better ...

With a portable generator, there is no way to assure a good connection between the generator and the ground you're standing on- if for no other reason than that the generator has rubber feet.

So you drive a ground rod. What have you accomplished, apart from taking 'portable' out of the equation?

No, our 'ground' is of interest only in clearing faults. That's where the ground wire, and the neutral/ground connection at the transfer switch comes into the picture. Any current that comes from the generator wants only to return to that generator - not to go anywhere else.

Joined: Aug 2010
Posts: 9
L
New Member
renosteinke - thanks for your reply. Your explanation of the ground returning to its source makes perfect sense and I agree completely. Another reason I don't like sharing the neutrals is that you're required to isolate the neutral and ground in the generator. Since it's portable, it can be used for other applications where an appliance or tool can be plugged directly into the generator. Would it be dangerous to use it like this with the neutral and ground isolated? Would the overload trip on a fault to the grounding wire? It would be easy for the user to forget to change this connection for each change of use.
Similar problem with connecting the generator to a GEC. Likely the generator will be stored elsewhere and moved to the house connection point when it's needed, requiring the user to remember to make that connection. And if the GEC is for handling overvoltage problems, where is the overvoltage going to come from anyway?

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I am still not sure where the danger is if the ground and neutral is isolated in a truly portable generator. The small Hondas are made this way. There is no real connection between the power and ground to provide the hazard.


Greg Fretwell
Joined: Nov 2000
Posts: 2,148
R
Member
While I don't see a hazard with the generators that do not have their neutral bonded, there is no way to use those in an NEC application because 250.20 will require a grounded system in most cases. As far as what is an NEC application, given the definition of premises wiring...most everything;


Don(resqcapt19)
Page 1 of 4 1 2 3 4

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5