#196500 - 10/09/10 04:55 AM Tray Cable
michelebacocchia Offline
New Member
Registered: 08/23/10
Posts: 6
Loc: Italy
Hello!!

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?

Thanks!
Top
Tools for Electricians:
#196507 - 10/09/10 11:55 AM Re: Tray Cable [Re: michelebacocchia]
twh Offline
Member
Registered: 03/11/04
Posts: 899
Loc: Regina, Sask.
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Ruben Rocha), 142 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals