The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured Items:

Switch Bit - Interchangeable Flex Bit System
>> Switch Bit -
Interchangeable Flex Bit System

>> 2014 NEC and Related

Recent Posts
Conduit penetration in top 3R Enclosure
by HotLine1
Today at 12:46 PM
Apprentice program
by Tesla
Yesterday at 02:43 PM
Waterfall Outlet
by wa2ise
11/24/14 06:40 PM
Bonding and grounding
by lite bulb
11/24/14 06:08 PM
Whirlpool tub grounding with pex
by renosteinke
11/23/14 05:19 PM
New in the Gallery:
Another find....
Shout Box

Top Posters (30 Days)
gfretwell 43
HotLine1 37
Tesla 14
renosteinke 10
BigB 8
Who's Online
0 registered (), 95 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#196500 - 10/09/10 04:55 AM Tray Cable
michelebacocchia Offline
New Member

Registered: 08/23/10
Posts: 6
Loc: Italy
Hello!!

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?

Thanks!

Top
2014 / 2011 NEC & Related Books and Study Guides
#196507 - 10/09/10 11:55 AM Re: Tray Cable [Re: michelebacocchia]
twh Offline
Member

Registered: 03/11/04
Posts: 794
Loc: Regina, Sask.
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.