The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured Items:

Switch Bit - Interchangeable Flex Bit System
>> Switch Bit -
Interchangeable Flex Bit System

>> 2014 NEC and Related

Recent Posts
Just gotta Say
by Webmaster
Yesterday at 08:40 AM
Overhead Span Across Portable Garage.
by wewire2
Yesterday at 08:37 AM
Minimum Bend Radius?
by HotLine1
07/17/14 06:47 PM
Coming off load side of meter twice??
by HotLine1
07/17/14 06:44 PM
Lock out /Tag Out Definition ((Affected person))
by Yoopersup
07/17/14 01:55 PM
New in the Gallery:
Copper Theft
Shout Box

Top Posters (30 Days)
HotLine1 35
Tesla 18
gfretwell 15
renosteinke 13
Lostazhell 8
Who's Online
0 registered (), 124 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#196500 - 10/09/10 04:55 AM Tray Cable
michelebacocchia Offline
New Member

Registered: 08/23/10
Posts: 6
Loc: Italy
Hello!!

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?

Thanks!

Top
2014 / 2011 NEC & Related Books and Study Guides
#196507 - 10/09/10 11:55 AM Re: Tray Cable [Re: michelebacocchia]
twh Offline
Member

Registered: 03/11/04
Posts: 791
Loc: Regina, Sask.
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.