The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


Recent Posts
Old British switches
by LongRunner
Today at 12:47 PM
When would you choose Al over Cu for an install?
by Texas_Ranger
11/24/15 05:20 AM
A Letter to the IAEI
11/24/15 02:45 AM
FPE Revisited
by HotLine1
11/22/15 12:35 PM
Swiss code violations
by Texas_Ranger
11/22/15 11:35 AM
New in the Gallery:
Access ??
Shout Box

Top Posters (30 Days)
gfretwell 25
HotLine1 19
renosteinke 15
Texas_Ranger 10
annemarie1 8
Who's Online
1 registered (cableguy619), 98 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#196500 - 10/09/10 04:55 AM Tray Cable
michelebacocchia Offline
New Member

Registered: 08/23/10
Posts: 6
Loc: Italy

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?


2014 / 2011 NEC & Related Books and Study Guides
#196507 - 10/09/10 11:55 AM Re: Tray Cable [Re: michelebacocchia]
twh Offline

Registered: 03/11/04
Posts: 846
Loc: Regina, Sask.
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.