The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
Looking for a unique adjustment nut
by HotLine1
Today at 07:14 AM
A taper or B taper, which is it?
by JoeTestingEngr
Today at 12:39 AM
GE low-voltage remote control relay system
by Albert
Yesterday at 10:26 PM
Electrical systems in mobile structures.
by gfretwell
Yesterday at 09:21 PM
Conduit Bending Apps for iPhone -Master Bender
by KJay
Yesterday at 08:31 PM
New in the Gallery:
A What's right here??
Shout Box

Top Posters (30 Days)
gfretwell 72
HotLine1 68
KJay 34
sparky 28
renosteinke 26
Classified Ads:


Electrical-Classifieds.com

Who's Online
1 registered (Albert), 119 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#195305 - 07/24/10 07:11 PM Another 680.26 water bond item
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
Another product surfaced Friday during inspections. Seems like there are a few mfgs jumping into the fray.

This is a carry over from Harolds thread.

Opinions, Gentlemen??

www.CMIwebsite.com

http://www.cmiwebsite.com/html/pool___spa-electrical.html (Page to look)





Edited by HotLine1 (07/24/10 07:14 PM)
Edit Reason: trying to insert right link
_________________________
John

Top
#195306 - 07/24/10 09:01 PM Re: Another 680.26 water bond item [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
You certainly want to go with the stainless one. It doesn't take much of a lapse on maintaining pool chemistry to have the water eat copper.
Certainly that neglect you see in a "closed" pool will do it.
_________________________
Greg Fretwell

Top
#195325 - 07/26/10 07:45 AM Re: Another 680.26 water bond item [Re: gfretwell]
harold endean Offline
Member

Registered: 02/16/02
Posts: 1813
Loc: Boonton, NJ
John,

I agree with Greg that I would use the SS one myself. It looks like these connections goes right onto the hoses from the pool filter, skimmer or return. I wonder if they will catch debris and clog up the line?

Top
#195328 - 07/26/10 11:00 AM Re: Another 680.26 water bond item [Re: harold endean]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
That is probably a good reason to put them downstream of the filter.

Who installs this? Electrician or pool plumber? wink
_________________________
Greg Fretwell

Top
#195331 - 07/26/10 03:28 PM Re: Another 680.26 water bond item [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
That could be another topic!!!

I have to ask the ECs IF the water bond device is 'on them', or the pool guy.

Might be a good subject?
_________________________
John

Top
#195335 - 07/26/10 06:56 PM Re: Another 680.26 water bond item [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
If I was the shop steward I would say the plumber puts in the fitting and the electrician hooks up the wire but I imagine the pool contractor does it all in most places.
_________________________
Greg Fretwell

Top
#195336 - 07/26/10 07:47 PM Re: Another 680.26 water bond item [Re: gfretwell]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
Greg:

I'm going to try this in a new thread
_________________________
John

Top
#195365 - 07/29/10 05:48 AM Re: Another 680.26 water bond item [Re: HotLine1]
sparky Offline
Member

Registered: 10/18/00
Posts: 5433




what is this?

~S~

Top
#195367 - 07/29/10 07:19 AM Re: Another 680.26 water bond item [Re: sparky]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4766
Loc: Brick, NJ USA
Another 680.26 (c) item to create 'stimulus' for a small business!
_________________________
John

Top
#195372 - 07/29/10 11:11 AM Re: Another 680.26 water bond item [Re: HotLine1]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7034
Loc: Estero,Fl,usa
Using table 9 and guessing that is 8ga wire (.128" diameter) that would have to be almost 23" long to get the required 9 sq/in
.128 x 3.14 x 23 = 9.244

_________________________
Greg Fretwell

Top