ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Another product surfaced Friday during inspections. Seems like there are a few mfgs jumping into the fray.

This is a carry over from Harolds thread.

Opinions, Gentlemen??

www.CMIwebsite.com

http://www.cmiwebsite.com/html/pool___spa-electrical.html (Page to look)




Last edited by HotLine1; 07/24/10 09:14 PM. Reason: trying to insert right link

John
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
You certainly want to go with the stainless one. It doesn't take much of a lapse on maintaining pool chemistry to have the water eat copper.
Certainly that neglect you see in a "closed" pool will do it.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
John,

I agree with Greg that I would use the SS one myself. It looks like these connections goes right onto the hoses from the pool filter, skimmer or return. I wonder if they will catch debris and clog up the line?

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
That is probably a good reason to put them downstream of the filter.

Who installs this? Electrician or pool plumber? wink


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
That could be another topic!!!

I have to ask the ECs IF the water bond device is 'on them', or the pool guy.

Might be a good subject?



John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
If I was the shop steward I would say the plumber puts in the fitting and the electrician hooks up the wire but I imagine the pool contractor does it all in most places.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:

I'm going to try this in a new thread


John
Joined: Oct 2000
Posts: 5,392
S
Member
[Linked Image from cmiwebsite.com]



what is this?

~S~

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Another 680.26 (c) item to create 'stimulus' for a small business!



John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Using table 9 and guessing that is 8ga wire (.128" diameter) that would have to be almost 23" long to get the required 9 sq/in
.128 x 3.14 x 23 = 9.244



Greg Fretwell