1 members (Scott35),
184
guests, and
13
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Nov 2007
Posts: 764
OP
Member
|
How are you interpreting “equipment grounding conductors, where installed,” as stated in 250.122[B] when ungrounded conductors are upsized? Do you consider this as meaning where an EGC is actually pulled in a raceway, or simply where any EGC is present, whether physically pulled or part of a listed cable assembly, such as SER?
It seems that this could possibly be interpreted either way and might allow using an upsized cable assembly containing an equipment-grounding conductor sized only per Table 250.122, as opposed to a raceway where the conductors are pulled and the EGC sized on the ratio of the circular mil area of the upsized ungrounded conductors. What is your take on this?
TKX
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
In a cable, the EGC size gets bigger in proportion to the other conductors getting bigger so 250.122(B) is satisfied. I assume that is built into the listing standard for all cables. In the case of SE cable (TYLZ in the white book) it says Based upon tests which have been made involving the maximum heating that can be produced, an uninsulated conductor employed in a service cable assembly is considered to have the same current-carrying capacity as the insulated conductors even though it may be smaller in size.
Greg Fretwell
|
|
|
|
Joined: Nov 2007
Posts: 764
OP
Member
|
Thank you Greg. Good find on the SE cable listing. I had considered that the cables must have had this rule applied already, but now that I have thought this through a bit more, it appears that since Table 250.122 is based on overcurrent, not wire size, it wouldn’t have any relevance when over sizing conductors for things such as voltage drop calcs, being that the actual overcurrent protection would normally be lower than the maximum rating of the conductor. Unfortunately, sometimes I’m not the sharpest tool in the shed.
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
The white book is a great resource if you are curious about the listing on a particular product. Unfortunately it usually ends up making you want to actually see the listing standard and U/L charges big bucks for that. I suppose that is why they give the White Book away for free.
Greg Fretwell
|
|
|
Posts: 99