#194454 06/03/10 03:23 PM
Joined: Oct 2002
Posts: 830
S
Member
I don't have a 2008 code available, only 2005. In the 2005 it says the clearance for service drops over a roof area is 8ft., with an exception of 3 feet where the roof pitch is 4 inches in 12 inches. Is this the same in the 2008 code? Thanks for the reply..

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Presuming that the voltage between conductors does not exceed 300 volts, 3 feet is still OK.